Say, there were a resistance between the main bond correctly installed at the point of entry and somewhere else in the house then surely the pipes on the consumer side of this resistance will not be sufficiently bonded.
Are you not overlooking the (
one and only) reason for main bonding - namely to prevent a PD arising within the house by virtue of a difference in potential between the house's MET and the potential introduced (from outside the premises) by an incoming service pipe?
That is they may, if long enough, still have an impedance between a fault and the bond and hence the MET. Is this not the same as not being at the same potential?
As above, although what you say is true, it is
not something which MPB is designed to address. MPB seeks only to prevent PDs arising because of potentials introduced from outside the property. Ironically, the hazard you are now describing may result from
not directly bonding the house's pipework to the MET (when the service
has been bonded prior to an 'insulating section') - something which many people (I think including yourself) have been known to argue is unnecessary, if not 'dangerous'.
Let's face it, the hypothetical situation I think you are postulating (of a meter which represents a finite. but neither very low nor very high, resistance) is merely a lesser example of the more extreme case of household pipework which is totally insulated/isolated from a bonded extraneous-c-p (e.g. by an 'insulating section'). I though we had agreed that, in such a situation, MPB considerations do
not require that pipework to be bonded
Is that why bonding on the consumer's side of meters is 'recommended'?
As I've said, if such bonding were required (by regs), which I don't think it is, it would be supplementary, rather than main, bonding.
[Surely if it is not extraneous at the entry to the property and so does not require bonding then it will not require bonding for the purposes of 701.415.2(v).
As I said, 701.415.2(vi) refers to "extraneous
to the location" and, as I also said, I have always taken that 'location' to mean the bathroom, not the property. That view is perhaps re-inforced by the fact that the title of Chapter 701 is "
Locations containing a bath or shower" - and you surely don't believe that 'location' there refers to the whole property, rather than just the bathroom?! I take it that you disagree with this interpretation?
If over 23kΩ between point of entry and MET won't it be >23kΩ between this pipe and other things in the bathroom?
That's surely the whole point. As I said, thanks to CPCs and exposed-conductive parts, one would expect metal pipework entering a bathroom to have probably <1Ω to the MET, not >23kΩ, wouldn't one?
Plus if the pipes are not isolated then they will/should be main bonded.
Will/should they? I thought that was what we were discussing. I thought we had agreed that if the service was main bonded at or near the point of entry, there was no need to main bond house pipework beyond a subsequent 'insulatting section' or whatever.
If it did not require main bonding then it won't require supplementary bonding so you would be introducing hazards by so doing.
This all depends on the interpretation of "extraneous to the location" in 701.415.2(vi), about which our views appear to differ!
Kind Regards, John