There is obviously nothing 'comprehensive' one can do about it, because fault currents (flowing from L to E) could theoretically have any value - from the 'PEFC' (which is what we have when we assume that the fault itself has zero impedance0 down to values which would be quite credible as 'L currents in normal operation'So what can be done about the situation for the infinite number of possible fault currents that people seem to think might exist when one stray wire touches something it should not? I feel we must be missing something.
One this which cab be (and is) done is to have the 'additional protection of RCDS, since an RCD will detect a tiny ("L-E") fault current.
In terms of ADS using OPDs, what surprises me is that they have not made at least some allowance for the fault impedance being finite (i.e. at least a little above zero) - even if only, say, 0.1Ω or 0.2Ω. If that were done, the tabulated 'maximum Zs' figures we work with would reduce by that amount. Let's face it, even a 'deliberate connection' is, in the real world, not going to have an impedance of 0.0000000...Ω, so it seems totally unrealistic and unreasonable to assume that the 'accidental touching' of two conductive parts will have a contact resistance as low as that.
Fair enough.I have said before I once blue the DNO 60A fuse when a stray T&E CPC happened to spring into the CU main switch line incomer screw. It did not stay there, of course, but was blown back immediately by the flash. Obviously the current must have been great enough for the instant disconnection with no damage to anything apart from a small globule melted on the end of the CPC and a mark on the screw.
I'm not sure what you mean by "faults of quite considerable resistance". A 1Ω fault would result in 230 A, which would blow a 60A fuse more-or-less 'instantly', wouldn't it?How then do these faults of quite considerable resistance manage to maintain contact for long enough if the disconnection is not 'instantaneous'?
The problem is that the impedance of the fault is very unpredictable. I've just done a quick experiment gently touching and stroking the end of a copper conductor against a bit of brass, and got resistance readings varying from <0.01Ω to about 5Ω.
Kind Regards, John