If Navien want to take a large chunk of UK market share they will.
24 foot of 1/2 pipe as the claim can not supply 57KW no matter what appliance is connected at the other endThe vid states using the negative pressure gas valve 24 foot of 1/2" (15mm) pipe can be used supplying a 200,000 BTU (57kW) combi. The post meter gas pressures in the USA are about the same as here. They say ~8" wc (wg - water gauge here). A 57kW combi in the UK would need a 28mm gas pipe for most of its run. Using 15mm is quite a saving in many respects. The 40kW combi gives ~16 litre per min of DHW.
Negative pressure gas valves are used on pre-mix burners. I don't know if Navien use negative pressure gas valves on the combis in the UK.
The vid at 1 min 40 secs states, using the negative pressure gas valve 24 foot of 1/2" (15mm) pipe can be used supplying a 200,000 BTU (57kW) combi. Not available in the UK
There's a good reason too.
I have already said why. As has another poster.
Venturis are/were used to get higher pressure in fire hoses to get pressure to the top of high ladders.
BTW, Baxi do not make that hydro block do they? I cannot see Navien buying from Bax