Evening,
Kid brother is after a new heating system and he's asked me for help speccing it. I'm after a sanity check here!
The house is a 130m^2 Wimpey house built in the late 1980s. Nominally insulated cavity wall construction with dabbed plasterboard, but the detailling is rubbish and it leaks heat like a sieve.
It presently has a "17kW" potterton suprima feeding single panel rads in a single zone (no TRVs but does have a room stat in the hall) and a vented hot water cylinder via two two-port zone valves. One shower via a pump from the HW cylinder and the CH header tank (yes!) and the other shower is electric.
Issues with the current system:
-electric showers are hopeless; two high pressure 12L/min with 5C mains inlet temperature showers are desired.
-the heating is inadequate both in ultimate output and response time; the ability to maintain 20C down to -5C external temperature is desired, and as the house leaks heat like a sieve and is unoccupied for significant parts of the day he'd like a system that allows it to drop to 10C, then can bump it to 20C in an hour or two for the 10 hrs/day that the house is actually occupied.
-one zone heats lots of the house unnecessarily; he'd like two zones; one bedrooms/bathrooms and another "other" zone - upstairs/downstairs essentially.
-the radiator sizing is all over the show and combined with a lack of TRVs means that the room temperatures are all over the show.
-It's a non-condensing boiler/ludicrously inefficient; boiler limits current radiator output but the rads would limit any larger boilers output.
I propose swapping all the rads for "oversize" double panel affairs. Providing that they're all equally oversized so that each room in the zone heats up evenly, am I correct in assuming that there's no problem with this bar the delta cost of the larger radiators?
I propose fitting one roomstat in the downstairs hall; one roomstat in the master bedroom. Reasonable?
Then we have options:
1) One system boiler, one pump, three 2-port valves, a programmer capable of running this lot, plus an unvented cylinder.
2) Two combi boilers with built in pumps etc. Run the upstairs and one bathroom as one zone/"house" and the downstairs/other bathroom and kitchen tap as another zone/"house" with each having their own programmer.
The latter appeals. Thanks to volume, an entire combi with all the gubbins built in costs about the same as an unvented cylinder and all associated pressure gubbins and zone valves.
The labour with the skills to bung in a combi vs fit an unvented cylinder and zoned system boiler is also cheaper. (we can install the water side in ourselves, fit the backplates, then have an RGI in to run the gas and hang/comission the boilers) Plenty more semi-qualified (capable of servicing one brand of boiler, but utterly hopeless at servicing/fault finding a "system" of components) service techs out there too.
The inevitable breakdowns/general servicing are also less of a showstopper, as you'll always have somewhere warm in the house/some hot water.
How daft is this? Seen it done elsewhere?
Concerns:
-Gas supply. The existing gas supply is f**king sketchy. A single 15 mm pipe ~12 metres in length feeds a 7kW heat input living room gas fire, 17kW boiler, and large (10+kW heat input) gas range. If the hob is lit on a low-medium output, it'll be extinguished when the boiler fires. Pipework after meter all needs replacing anyhow, so the options are equal here anyhow. The supplier is arranging a "GT1" test for the gas to see what pressures/flows are available. At the minute it has a U6 meter; U16 would be required for this setup, correct?
-Water supply. The existing water supply to the house appears good. (>24L/min on an open pipe via the 15 mm stoptap and meter, no doubt more when the stoptap is replaced with a large dia MDPE one and the supplies branched in 15 mm after this)
-Boiler *minimum* output in CH mode. To get 12L/minute with 5C input we're looking at large combis. 10:1 modulation is still 4kW minimum output. No problem in winter as the heat loss exceeds this comfortably. No problem in summer as it'd need just a quick "boost" then a low heat loss/some thermostat hysterewsis would prevent the boiler firing too often. Spring/autumn are a concern. How short a cycle is "too short" for a boiler?
I'm looking a pair of Vokera Linea Ones (fitted in the attic space) for around 3k the pair inc sundries at present:
http://www.vokera.co.uk/trade-professionals/boilers/linea-one/
Includes modulating pump, gunk filter, filling loop, weather comp heating control, frpst stat, predictive DHW control for preheat etc - just add water, gas, expansion vessel, and radiators?
Kid brother is after a new heating system and he's asked me for help speccing it. I'm after a sanity check here!
The house is a 130m^2 Wimpey house built in the late 1980s. Nominally insulated cavity wall construction with dabbed plasterboard, but the detailling is rubbish and it leaks heat like a sieve.
It presently has a "17kW" potterton suprima feeding single panel rads in a single zone (no TRVs but does have a room stat in the hall) and a vented hot water cylinder via two two-port zone valves. One shower via a pump from the HW cylinder and the CH header tank (yes!) and the other shower is electric.
Issues with the current system:
-electric showers are hopeless; two high pressure 12L/min with 5C mains inlet temperature showers are desired.
-the heating is inadequate both in ultimate output and response time; the ability to maintain 20C down to -5C external temperature is desired, and as the house leaks heat like a sieve and is unoccupied for significant parts of the day he'd like a system that allows it to drop to 10C, then can bump it to 20C in an hour or two for the 10 hrs/day that the house is actually occupied.
-one zone heats lots of the house unnecessarily; he'd like two zones; one bedrooms/bathrooms and another "other" zone - upstairs/downstairs essentially.
-the radiator sizing is all over the show and combined with a lack of TRVs means that the room temperatures are all over the show.
-It's a non-condensing boiler/ludicrously inefficient; boiler limits current radiator output but the rads would limit any larger boilers output.
I propose swapping all the rads for "oversize" double panel affairs. Providing that they're all equally oversized so that each room in the zone heats up evenly, am I correct in assuming that there's no problem with this bar the delta cost of the larger radiators?
I propose fitting one roomstat in the downstairs hall; one roomstat in the master bedroom. Reasonable?
Then we have options:
1) One system boiler, one pump, three 2-port valves, a programmer capable of running this lot, plus an unvented cylinder.
2) Two combi boilers with built in pumps etc. Run the upstairs and one bathroom as one zone/"house" and the downstairs/other bathroom and kitchen tap as another zone/"house" with each having their own programmer.
The latter appeals. Thanks to volume, an entire combi with all the gubbins built in costs about the same as an unvented cylinder and all associated pressure gubbins and zone valves.
The labour with the skills to bung in a combi vs fit an unvented cylinder and zoned system boiler is also cheaper. (we can install the water side in ourselves, fit the backplates, then have an RGI in to run the gas and hang/comission the boilers) Plenty more semi-qualified (capable of servicing one brand of boiler, but utterly hopeless at servicing/fault finding a "system" of components) service techs out there too.
The inevitable breakdowns/general servicing are also less of a showstopper, as you'll always have somewhere warm in the house/some hot water.
How daft is this? Seen it done elsewhere?
Concerns:
-Gas supply. The existing gas supply is f**king sketchy. A single 15 mm pipe ~12 metres in length feeds a 7kW heat input living room gas fire, 17kW boiler, and large (10+kW heat input) gas range. If the hob is lit on a low-medium output, it'll be extinguished when the boiler fires. Pipework after meter all needs replacing anyhow, so the options are equal here anyhow. The supplier is arranging a "GT1" test for the gas to see what pressures/flows are available. At the minute it has a U6 meter; U16 would be required for this setup, correct?
-Water supply. The existing water supply to the house appears good. (>24L/min on an open pipe via the 15 mm stoptap and meter, no doubt more when the stoptap is replaced with a large dia MDPE one and the supplies branched in 15 mm after this)
-Boiler *minimum* output in CH mode. To get 12L/minute with 5C input we're looking at large combis. 10:1 modulation is still 4kW minimum output. No problem in winter as the heat loss exceeds this comfortably. No problem in summer as it'd need just a quick "boost" then a low heat loss/some thermostat hysterewsis would prevent the boiler firing too often. Spring/autumn are a concern. How short a cycle is "too short" for a boiler?
I'm looking a pair of Vokera Linea Ones (fitted in the attic space) for around 3k the pair inc sundries at present:
http://www.vokera.co.uk/trade-professionals/boilers/linea-one/
Includes modulating pump, gunk filter, filling loop, weather comp heating control, frpst stat, predictive DHW control for preheat etc - just add water, gas, expansion vessel, and radiators?