To OP.
It might be worth redoing some of it properly since I suspect you are redecorating and thus there is little downside to doing so. Better than using undersized terminal blocks or incorrectly performing crimps (require ratchet tool). Not sure how you have found space to fit a terminal block in a 25mm box without crushing insulation.
1. Backboxes.
- With 2 cables - 25mm box possible, 35mm preferable
- With 3 cables - 35mm box everytime
Some wiring accessories require 35mm (eg, MK sw fused spur).
Likewise lighting often uses 16mm, but dimmers often need 25mm.
2. Terminal connectors
- Whilst meeting "accessible" regs, it is not ideal
- 380V is irrelevant, the *current rating* is critical
- For a 32A CPD you need connector blocks rated to 32A
- This makes them bigger, hence my suggestion to redo it
3. Crimps.
- Crimps are a better & more compact connection method
- Crimps require a proper ratchet tool & care with solid core cable
- Proper crimps & tool will set you back 25ukp
Plier type tools will not produce an acceptable crimp.
Hence cheapest solution is just to redo them.
> I then had a a very difficult job pushing the sockets in,
> but all the plugs are working.
Working does not mean EFLI & IR are still ok.
That is why good workmanship & correct materials is so important.
Sounds like you are redecorating as well?
I urge you to...
- redo the boxes to avoid terminal blocks
- preferably using 35mm boxes where there are 3-cables
- move the boxes slightly if necessary to gain cable length if need be
If the wall is block (light grey breeze, dark black coke cinder)
- Do not SDS
- Use a masonry bit with hammer turned off
- Mark out an outline of the backbox & "stitch drill" around it & within it
- Gently break out/chip out the area
If doing backboxes into internal block, note it can be as little as 70mm.
So with 25/35mm deep boxes it is important not to put them back to back
Additionally cutting the block should be done gently, hence I prefer 20mm diamond core bits in a cordless drill to do overlapping holes. Very quick, controlled. Less brutal than a SDS "socket sinker" where slim block walls are on floorboards perpendicular to joists and thus "bouncy".
If the wall is soft brick
- SDS on low speed, don't use a single speed chisel (too brutal)
- Or, narrow hand chisel & lump hammer, slow, but not that slow
- Or, stitch drill with a masonry bit as with block
Some bricks can be almost like sandstone and a screwdriver with a tap will scrape out a backbox. Realise the rest of the wall provides support, just do not break through to the cavity if present on an outside wall. If you do, repair with cement, but do not bridge the cavity with it.
I would not worry about having to move backboxes if need be to avoid terminal blocks, you are only introducing a future failure point. Will only cost you 90p a backbox to redo it, then you know it is done right.