People don't have decent crimp tools.Properly crimped with a decent tool, there is no issue with solid core cable.
I cannot make out what's what in your picture - but it doesn't look too good.
People don't have decent crimp tools.Properly crimped with a decent tool, there is no issue with solid core cable.
Certainly MOD spec in the 70s forbade solid crimpingI was certainly brought up to believe that solid conductors shouldtonot be crimped and, as discussed here before, at least one set of Standards/'rules' (those applicable to NASA) says that, but I'm not personally aware of any rules/regulations applicable to UK electrical installations which actually 'forbid' it.
Personally speaking, I'm not totally comfortable with the practice - but that's just me!
Kind Regards, John
Edit: typo corrected
Yes, of course, in the hands of someone experienced, with appropriate tools, it seems to very rarely 'result in an issue'. However, as always, 'very rarely' is not necessarily the same as 'never' ...I’ve been crimping solid cores for 20+ years and never had an issue.
People don't have decent crimp tools.
I cannot make out what's what in your picture - but it doesn't look too good.
I don't think it's the extent to which the copper fills the shape of the crimp that is necessarily the issue - it's the quality (in both short- and long-term) of the contact between conductor and crimp that matters. As you have said, copper is very soft and, unless a stable 'cold weld' is created, it can 'creep' when it is under some pressure - potentially leading to a situation comparable with a screw terminal which has been tightened only very 'loosely'.It's essentially a perfect crimp, some of the artefacts are due to the shear cut through the crimp terminal, but you can see there is exact deformation of the copper to fill the shape of the crimp.
I don't think it's the extent to which the copper fills the shape of the crimp that is necessarily the issue - it's the quality (in both short- and long-term) of the contact between conductor and crimp that matters. As you have said, copper is very soft and, unless a stable 'cold weld' is created, it can 'creep' when it is under some pressure - potentially leading to a situation comparable with a screw terminal which has been tightened only very 'loosely'.
I think we are all agreed that a properly executed crimped joint on a solid conductor will 'nearly always' be fine - but that leaves the question of what 'nearly always' actually means.
Kind Regards, John
Along the length of the conductor. If one applies appreciable pressure to the sides of a conductor, some copper will 'ooze' out beyond the ends of the region of compression. A similar phenomenon can occur with 'creep', at much lower pressures. Try it with Plasticine if you have any doubtsWhere is the copper going though if it's filled the crimp?
That's something I'm not so sure about - but it is one version of 'traditional wisdom'.How is the situation different for stranded conductors?
Where's your grommets, Gaz!
In case anyone here missed, or has forgotten, the past discussions, the NASA's "Workmanship Standard for Crimping ...." can be found here . I would draw particular intention to 7.2.26 on page 24 (of 101), which says ...NASA's concerns presumably relate primarily to very high levels of vibration and, in that context, something seems to have convinced them that crimping stranded, but not solid, conductors is OK.
They clearly want to make their point since, having written (a), they did not really need to underline it with (b) and (c)!NASA said:7.2.26 The following requirements apply for crimped connections.
a. Crimped contacts shall be used with stranded wire only.
b. Solid wire shall not be used with crimped contacts.
c. Solid, tinned wire shall not be used in crimped contacts
Possibly, and I wasn't really intending to cite them as being divine or omniscient - merely indicating that they were one organisation which, for whatever reason, forbade crimping of solid conductors.Not sure NASA is any particular standard for excellence
No he didn't.Or is there another, better, perhaps safer method which falls short of replacing an entire run of cable? This is a house with solid floors.
Soldering, then covering the joint with heat shrink or self amalgamating tape.