Although AC travels in both directions with the incomer at bottom the contact (3) isolate most of the device, so that is the preferred method, as to RCD it states in quite a lot of information for example Wylex this must be double pole.
Wylex Solar PV 2 said:
411.3.2.2
The maximum disconnection time shown in Table 41.1 applies to circuits not exceeding 32A. 0.4 s TN System & 0.2 s TT Systems.
551.4.1
Fault protection shall be provided for of each source of supply or combination of sources of supply.
(Also, refer to chapter 55, regulation group 551- Low Voltage Generating Sets)
551.5.1
Over current protection should be located as near as practical to the generator terminals (where required).
712.537.2.1.1
To allow maintenance of the PV Inverter, means of isolating the PV inverter from the DC side and the AC side shall be provided.
(Also, refer to chapter 53, regulation group 537- Isolation and Switching)
712.434.1
The PV supply cable (AC side) shall be protected against fault current by an overcurrent protective device installed at the connection to the AC mains.
Also, refer to Part 7, all regulations in Section 712 - Solar Photovoltaic (PV) Power Supply Systems)
712.411.3.2.1.1
The PV Supply cable (on the AC side) shall be connected to the supply side of the protective device for automatic disconnection of circuits supplying current - using equipment.
314.1
Every installation shall be divided into circuits as necessary to : (ii) facilitate safe inspection testing & maintenance (vi) prevent the indirect energising of a circuit intended to be isolated.
314.4
In an installation comprising more than one final circuit, each final circuit shall be connected to a separate way in a distribution board.
The wiring of each final circuit shall be electrically separate from that of every other final circuit, so as to prevent the indirect energising of a final circuit intended to be isolated.
522.6.101 522.6.102 & 522.6.103
Installers must consider the need for Additional Protection by 30mA RCD in accordance with regulations (Previously 522.6.6 & 522.6.8) that relate to concealed cables in walls
& partitions.
The
Best practice guide refers to problem when RCD not double pole.
I looked for disconnection times, it seems the PV array has to disconnect if the voltage goes too high or too low or the frequency goes too high or too low, it is considered if the mains supply is lost either the voltage or frequency will go out of the limits and so fail, there are times quoted as to how fast it must close down if the limits are exceeded, however the problem is until those limits are exceeded there is not time to disconnect. So in real terms no one can state with a power failure how long it will take for the PV supply to exceed the limits, it would depend on load and how much sun etc. So it may be within 0.1 seconds when tested once, but will it be within 0.1 seconds with all tests if test infinity time?
Since no one can answer that question, the PV needs to supply the consumer unit with a double pole RCD. Here we are down to makes, some manufacturers make single width RBCO's with double pole switching, others need two modular spaces to fit such a device.
So if you want to cross every t and dot every i then likely you need a lot more than if you do a risk assessment and work out what is reasonable. Voltage tripping is a real problem with a PV install, we saw the voltage officially drop from 240 to 230 volt, but in real terms it stayed at 240 volt, until solar panels arrived that is. At 240 volt it was all too easy to trip out the panels due to over voltage, so we have seen areas drop to 230 volt simply to cater for solar panels.
I am quite sure a RCD tripping would quickly cause a solar panel grid tie inverter to quickly shut down, but with solar panels on half the houses in a street, how quickly a loss of supply would cause them to close down is a subject for debate. Each house will likely have slightly different limits set, so how long before they all trip, and if that time will be long enough for some panels to auto re-energise is a question that could be debated until the cows come home.