And also, presumably, from those Henley blocks up through the conduit to the meter for the upstairs property.The previous electrical supply comes up through the ground via metal conduit and is terminated into henley blocks inside metal trunking, then into the meter.
Surely that's their cable?The UKPN cutout will be in that burnt out cupboard once it is rebuilt. I am running a cable from the cutout to the meter.
?I was thinking of installing a 60amp wylex isolator supplying 16mm 3 core swa. The run is about 15m long. Is there any problem with this or will the swa need to 25mm?
Quite so - and particularly if (as sounds to be the plan) the cable eminating from it disappears into some trunking and then reappears a few meters later to be connected to the supply-side of the meter!I can't believe the DNO are happy to let you use a switchfuse like that. It is open to abuse.
If the work involves DNO stuff then they should give you a permit to work.
Well a good starter for ten would be to explain to the spark exactly what is required.This looks like a typical council "legacy" job that the DNO is trying to make the best of a bad job out of.
UKPN will not renew the cables to the two properties, only to the cutout. The cable from the isolator that i want to install to the meter will belong to the council. Is this unusual? I've had a job before in an where an isolator had to be renewed in an intake cupboard, UKPN said that did not own the isolator or the cable from it to the meter in the flat. The council was given permission to remove the main fuses to the building so that the work could be completed.
The main thing that i wanted to know is if they would insist on a 25mm cable even though I would be supplying a 60amp switchfuse.
Thanks anyway and apologies if you did not understand what I was talking about.
Why not just one cutout (the first one) with the 80A or 60A fuse - is what you say just so that there is a fuse (usable for isolation) close to the meter (and probably CU)? In terms of faults, I wouldn't think you'd get much discrimination between 80A and 100A fuses, would you?In the situation you describe, I would put 100A fuse in 1st cut out, run 35mm Al LS0H Orange split concentric cable (to comply with G81). We would install a second Henley cutout next to meter with 80A or 60A fuse. Both cut outs would be sealed.
I still find it odd that a DNO would request a device to make theft nice and easy.