If they're both in the same oven/cavity, yes, but ....They won't be cycling independantly. The thermostat will switch them both on and off together.I'm a bit lost here. What is the difference (other than the obvious!) between two elements cycling independently
This appears to be the problem. You don't seem to accept that diversity can apply across time (even if there is only a single, time-cycling, load) as well as 'space' (multiple loads, independently cycling). If you continue not to accept this, I fear that the discussion probably cannot progress ...Would it? I am saying "No".Indeed, the (OSG) diversity formula everyone seems to use would be applicable to a single 4.68 kW element which was time-cycling, wouldn't it?
... consider some simple hypothetical situations (using the previous example numbers). Firstly, two 2.34 kW (at 240V) elements (say hobs), each drawing about 9.34 (so 18.68A when both were on), each independently time-cycled by a thermostat such that they had an approximately 50/50 on/off ratio. Over any moderate period of time, the time-averaged current would be approximately 9.34A (although the maximum instantaneous current will still be 18.68A, at some points in time). That is why diversity is allowed, and you would presumably accept that.
Secondly, consider a single 4.68 kW (18.68A at 230V) element, again time-cycled by a thermostat such that it had an approximately 50/50 on/off ratio. Again, over any moderate period of time, the time-averaged current would be approximately 9.34A (and the instantaneous current either 18.68A or zero). However, if I understand what you're saying, in this situation you would not accept the application of diversity, despite the time-averaged current being exactly the same as in the first scenario. If I'm understanding you correctly, can you perhaps explain the basis of your reasoning?
Seemingly. Where, for example, in the regs will you find a requirement for fans fed from 6A lighting circuits to have 3A FCUs or 3-pole isolators?Intentionally?Well, yes, the regs themselves are obviously not retrospective - but manufacturers can (and often do) 'go beyond the regs'!
Which is presumably not totally immune from being broken.However, the shower itself has an all plastic exterior.
KindRegards, John