Yes, it was not the actual plug I was against but that it has a 13A fuse.
You think not (because it does not contain more than one 'independently cycling elements') - so I presume you would say the same if there were no plug, but, rather a dedicated hard-wired circuit with a hypothetical 13A MCB - is that the case?
Well, yes - as above - but it would seem I must concede.
No-one, and certainly not me, wants you to concede unless you are actually convinced, and it sounds as if you aren't! As I've tried to explain, I'm not convinced by my (different) view, either, since I don't know what we are most concerned about - average current over time, proportion of time with current >I
n of the OPD, a combination of the two, or what.
Having said that, diversity, be it for cookers, lighting circuits or whole installations only ever considers multiple loads and the premise that they are not all on/used at the same time; nowhere, apart from the quotes from Bas , does anywhere mention the time factor or rather how to allow for this.
Again, it depends upon what one's criteria are.
IF one is interested in average current over time, then "multiple loads which are not all on at the same time" is no different from 'one load which is not on all the time'. On the other hand, if one were interested in the proportion of time with current >I
n of the OPD, that would, indeed, usually be greater with the single load than with multiple 'independent' loads. As I've said, I don't know which of these is the more relevant to a diversity calculation.
As for the original question, I still cannot see it is right that the design current for a single 20A load can be 13A (10A + 30%) ...
In case it's not obvious, I can sympathise with your view - but I think it's probably more quantitative than conceptual. What if it were two, independently cycling, 10A loads? If the on/off duty cycle were the same for those two loads (and the same as the duty cycle for the single load), the average total current over time would be the same as with a single 20A load, and the main difference would be that the proportion of time for which current was >I
n with the single 20A load would be double the proportion with the 2 x 10A loads. ... so it might be, for example, that total current was >I
n for 40% of time for the single load and 20% of the time for the two loads - but would that, in your mind, necessarily make the difference between 'unacceptable' and 'OK'?
Kind Regards, John