Whilst that might be true, isn't it the case that manufacturers will size the lead and make equipment suitable for where they know it will be connected?We know that, although some people may 'argue'. In fact, provided only that the OPD is adequate to protect the fixed wiring, there's absolutely no reason why someone could not use an OPD rated to satisfy any perceived need for protraction of connected equipment - although that would often/.usually result in an unnecessarily restrictive' OPD rating.
Unless a separate item is manufactured for the UK, then that for a 16A circuit.
Surely that relates only to the rating of plug fuse fitted - so 13A maximum OPD.That's a bit different. Whilst the 'Wiring Regulations, per se, relate primarily only to the 'fixed wiring' of the installation, there are also requirements for adequate protection of flexible cables 'plugged into' that installation.
True, but do you not think that is taken into account in manufacture?To be a little pedantic, it takes at least about 22A to 'blow' a 13A BS1362 (in-plug) fuse, so does not "limit the current to 13A".
Unlikely to be found in a dwelling, but -Yes, but you are now talking ('catastrophic overloads') with what we call 'faults', not overloads. The potential problem (for the flexible cables) relates to 'non-catastrophic overloads', A 32A MCB will allow up to about *** (??? - 36.16A) to flow indefintely, and higher currents than that for appreciable periods of time. If connected equipment results in a high overload current (e.g. an appliance with a 'jammed' large motor) then the flexible cable supply it could find itself carry high currents (much higher than its theoretical 'CCC') for at least long periods, maybe 'indefinitely'. Connection of such an appliance with nothing but a 32A MCB protecting its flexible cable would therefore not be regarded as acceptable in thee UK.
unless, of course, a cable with a CCC of 32A is used.