So that would mean you could not connect for example a 45A isolator or a flex outlet plate to a rfc as they are not BS1363, sounds like nonsense to me!
Correct.
A lolipop circuit using a 45A isolator is a technical non compliance, and you shouldn't be connecting flex outlets directly to a ring circuit anyway.
How do you connect a blank plate?
I have many times talked about the lollipop idea and I am not sure if it complies or not. APPENDIX 15 is only informative although most would look at it as part of the regulations but regulations states:
433.1.5 Accessories to BS 1363 may be supplied through a ring final circuit. With or without unfused spurs, protected by a 30 A or 32 A protective device complying with BS 88-2.2. BS 88-6. BS 1361. BS 3036, BS EN 60898, BS EN 60947-2 or BS EN 61009-1 (RCBO). The circuit shall be wired with copper conductors having line and neutral conductors with a minimum cross-sectional area of 2.5 mm² except for two-core mineral insulated cables complying with BS EN 60702-1, for which the minimum cross-sectional area is 1.5 mm². Such circuits are deemed to meet the requirements of Regulation 433.1.1 if the current-carrying, capacity (Iz) of the cable is not less than 20 A and if. under the intended conditions of use, the load current in any part of the circuit is unlikely to exceed for long periods the current-carrying capacity (Iz) of the cable.
The main bit here is:-
1) 30 A or 32 A protective device even if one was to use 4mm² cable as a ring you could not up the rating to 40A MCB it only applies to a 30 A or 32 A protective device no other.
2) capacity (Iz) of the cable is not less than 20 A is second thing so any part Reference Method 101 would need 4mm² cable and Reference Method 103 needs 6mm² cable.
With the feed to the lollipop using 6mm² cable Reference Method 100 I would not consider that cable as being part of the ring final and therefore will not come under 433.1.5 or APPENDIX 15 but the latter states "A ring final circuit starts and finishes at the distribution board" and so to comply we must consider the isolator or cooker connection unit used to connect the ring final 2.5mm² to the feed 6mm² feed as a distribution board and personally I see no reason why not but this has to be a personal decision and I can see how others may not agree.
Where the person installing is the person writing out the installation certificate (EIC) I see very few problems however where some one else is doing the electrical installation condition report (EICR) and submitting it to the LABC I can see where they would be loathed to accept it although since I can't really see how they could give it any code I can't really see how it could fail.
However a figure of 8 is another thing and historically that has always been a failure as it clearly does not start and finish at the distribution board?
Returning to original question first there has to be a question as this would change the answer given. Is the ring already RCD protected and what other protection device is in place (Fuse/MCB)?
TABLE 41.2 and TABLE 41.3 gives a range of acceptable maximum ELI readings from 1.04 to 1.19 for fuse and 1.44 to 0.36 for a MCB/RCBO depending on type used. If the ELI at near centre point of ring with a B32 MCB was for example 1Ω the there would be little problem extending the ring but at 1.42Ω it would not comply once extended.
However a 13A fuse is rated at 2.42Ω for earth loop impedance so very unlikely a fused spur would fail. Also one can get RCD FCU which if not already RCD protected would also get around that problem.
The problem remaining is running two large units from a single fuse could use a twin back box and two FCU's or grid switch with fuse and two cables or cross your fingers and use one and hope the fuse does not blow. Personally I would not expect the fuse would blow but of course if wrong then you will need to run a second fused spur and your taking chance not me.
I think PrenticeBoyofDerry has given a reasonable answer but what you have to remember it's a personal thing not simply quoting regulations and also as electricians we carry a ELI meter and can quickly plug it in and test although there are cheap testers for around £50 these are go/no go testers and will not tell you if there is any latitude to extend one a go/no go reading so only after you have finished will it show if OK or not which is a bit late.
If I was a DIY guy without a full set of meters then I think I would end up with loads a FCU's as without test equipment it's the most likely way to ensure all is OK. In theory we should always test ELI and RCD both mA and ms trip currents and times and insulation tests as well and we should be completing a Minor Works Certificate. (If it needs an Electrical Installation certificate then it will also come under Part P) However I realise many DIY people do not do this hence why I say use FCU. If you can measure the ELI then the answer would be different.