At last, something approaching common sense. Thanks for telling us!Amendment 2 allows this. ... The useless 'power vs lighting' shambles is gone, minimum size for any circuit is 1.0mm² copper.
Kind Regards, John
At last, something approaching common sense. Thanks for telling us!Amendment 2 allows this. ... The useless 'power vs lighting' shambles is gone, minimum size for any circuit is 1.0mm² copper.
Yes, that was why I mentioned T&E with regard to the inconsistencies:You can still use 1.5mm² MICC for ring finals, I believe.
I suppose it depends upon exactly how one reads it but, whilst (as we have often discussed) it doesn't seem rational, I wouldn't say that it is 'inconsistent' ...Yes, that was why I mentioned T&E with regard to the inconsistencies: For T&E, 433.1.204 states a 2.5mm² csa minimum but then goes on to state that "Such circuits are deemed to meet the requirements of Regulation 433.1.1 [protection of conductors] if the current-carrying capacity (Iz) of the cable is not less than 20 A" - i.e. 1.5mm² T&E.
Quite so. I can but assume that what flameport has told us is true (I'm still waiting for my Amd3 to arrive!) in which case, as I recently wrote, it seems to open up the possibility (maybe for "Europhiles"!) to have 16A radials wired in 1.0 mm² cable!All hail the new rule! ... We did calculations at college on how small we could go with the CSA. One such calc was 1 milli on an immersion circuit. ... I think we even did a stand-alone cooker on a 25A breaker using 2.5 milli.
I doubt that was the intention - I was merely observing that the change means that anyone with 'European inclinations' probably could now install 1.0mm 16A radials if they wanted to!Well, I'm not happy. FFS, you think Brexit would take us away from Euroing our British regs, not add more mindless Eurotrash regs.
I fear you will never be happy, thenI won't be happy until we've gone back to red/black imperial sized cable with VOELCBs. ... Proper British stuff! Britannia rules the waves. Hurrah!
D'oh, you and your quaint little British ways.Well, I'm not happy. FFS, you think Brexit would take us away from Euroing our British regs, not add more mindless Eurotrash regs.
I won't be happy until we've gone back to red/black imperial sized cable with VOELCBs.
Proper British stuff!
Britannia rules the waves. Hurrah!
Indeed - or, conversely, as I recently suggested, if one took a standard UK ring final and replaced the 32A MCB/RCBO with a 40A or 50A one, I suspect that the chance of their ever being any significant/serious problems would be incredibly small.Replace one of the ring circuit 32A MCBs/RCBOs with a 25A one (yes, I know they are not available for all CUs, but that just leads to the question of why not? - So only do it if one is available and of course installation method allows).
Heavens above; perhaps you could even try a 20A one if not a massive demand. ... Carry on as normal and see if anything noticeable happens.
If not then this would indicate that the British ring final circuit with all its special dispensations and restrictions is indeed redundant ...
I agree, but that is not allowed in the regulation - with separate rules for conductors in parallel.Indeed - or, conversely, as I recently suggested, if one took a standard UK ring final and replaced the 32A MCB/RCBO with a 40A or 50A one, I suspect that the chance of their ever being any significant/serious problems would be incredibly small.
Lines removed with what I have suggested.However, as I also said, to some extent one probably has to consider 'what is possible', even if extremely unlikley - so (in common sense terms) it all comes down to where one draws the line in the sand.
The question is how many real-world circuits are "Method C with no grouping or other derating factors" throughout. A particular elephant in the room that seems to be widely ignored is the grouping of conductors as they converge on the CU/DB. Granted not all of the circuits entering a CU/DB will be under full load at any given time but it's not improbable that several of them will be.Yes, I know - installation methods - but that is the same for every circuit.
Sure - but, as I presume you understand, what I was suggesting was that it's pretty (probably very) unlikely that a 2.5mm ring (or even, probably, a 2.5mm radial) would, 'in real-world practice', be likely to be subjected to a current high enough, and for long enough, top result in any significant harm/[problem, even if the 'overload protection' was way above the Iz of the cable (or even if there were no 'overload protection' at all) - so very probably 'no problem provided that there were adequate fault protection (which a B40 or B50 would probably provide).I agree, but that is not allowed in the regulation - with separate rules for conductors in parallel.
I would have thought so. Isn't the point that if cable is within any sort of 'conduit' which is buried in masonry, then at least some of the cable will be surrounded by air, rather than being in direct physical contact with the masonry? ... and that's as true with oval conduit as it is with any other sort of conduit/'tube'/whatever.Incidentally, something I have never been quite sure about: Is oval conduit buried in masonry regarded as method B?
At risk of attracting flak, I would personally say that this is where most people probably exercise 'common sense' - i.e. 'ignore' such small local instances of what is technically 'grouping' (which would lead to a high proportion of circuits, which were otherwise Method C, strictly not being Method C throughout their entire length). ... and it's not just in the vicinity of CUs/DBs - cables can often be in very close proximity, sometimes contact, for s very short distance when they enter accessories/equipment etc.The question is how many real-world circuits are "Method C with no grouping or other derating factors" throughout. A particular elephant in the room that seems to be widely ignored is the grouping of conductors as they converge on the CU/DB. Granted not all of the circuits entering a CU/DB will be under full load at any given time but it's not improbable that several of them will be.
Most ?The question is how many real-world circuits are "Method C
In a domestic situation as far as grouping - all ?with no grouping
Very few - or install them another way.or other derating factors" throughout.
In a usual domestic situation then if the cables are side by side flat on a wall in free air or buried in masonry, then grouping factors are unlikely to be necessary.A particular elephant in the room that seems to be widely ignored is the grouping of conductors as they converge on the CU/DB. Granted not all of the circuits entering a CU/DB will be under full load at any given time but it's not improbable that several of them will be.