When you're trying to work out how a DIYer has bridged the ring or connected a ring within a ring or some other such lash-up, it's a right royal PITA.
Yes I agree... But they do all that on radials too.When you're trying to work out how a DIYer has bridged the ring or connected a ring within a ring or some other such lash-up, it's a right royal PITA.
It does - but, on the other hand, one could have two 25A radials (assuming Method C).Well, it only takes two 16A radials to replace one 32A circuit and
One could, but how many homes are installed using Method C?It does - but, on the other hand, one could have two 25A radials (assuming Method C).
So What?With 30A BS3036 fuses, ring finals were/are a good idea; ...
Since the introduction of MCBs, the regulation has not been updated and rings are still regulated for 3036 fuses.
40A MCBs could easily be allowed for a standard ring giving even more capacity that would not be used.
One could,
Not if your house doesn't have wooden walls... unless I'm not up to date on the methods.One could
Indeed, one would need to do that to make me more comfortable.And to prevent that from happening you need to install more circuits.
Quite - heading for the situation in which each and every socket would be on its own dedicated circuit - but I find it hard to see that any perceived advantages would outweigh the installation and environmental) costs of such an approach (as compared with a smaller number of higher-current circuits).So rather than your 32A kitchen ring being replaced with two 16A or 20A radials, you end up replacing it with four or so, one for the washing machine, one for the dishwasher, one for the tumble drier and one for the rest.
What?Not if your house doesn't have wooden walls... unless I'm not up to date on the methods.
I'm not sure why you say that. Apart from anything else, as I've said my personal view about radials vs.rings is very 'neutral', so I'm not sure how I could 'negate' that!I think you've just negated your point of view.
I don't understand that statement. For a start, as I've said, I personally don't like 20A (let alone 16A) radials, so I would replace one 32A ring with one 32A radial. My 'discomfort is nothing to do with the type of circuit (ring or radial) but, rather, about the total capacity of a circuit which has multiple sockets - so I'm happy with any sort of 32A circuit.However as in posts #83 & #87 and your #82 (quoted) straightaway there is a requirement for more than 2 radials to replace one ring.
As I just wrote to plugwash, he (and to some extent you) are talking of moving in the direction of 'one socket per circuit' - which, although it would be a "designer's dream" has plenty of downsides.The last thing I want to see is the massive CU's our foreign cousins have to find a home for.
True, albeit 25A MCBs/RCBOs are often hard to find.It does - but, on the other hand, one could have two 25A radials (assuming Method C).
I'm surprised because actually I haven't come across the same abuse on a radial.Yes I agree... But they do all that on radials too.
I'm also surprised, since it's not easy to think of many ways is which someone might 'abuse' a radial. I suppose they might run a multi-socket branch in 2.5mm² cable from a 4mm² 32A radial (just as they could do with an unfused spur from a ring). I also suppose that it's just about conceivable that (as Sunray seemed to be suggesting), they think that two radials are a 'broken ring' and therefore connect them together, but that would seem very unlikley. Beyond that, I can't really think of anything.I'm surprised because actually I haven't come across the same abuse on a radial.
Yes, that's far from unknown but, provided all the cables are suitable, there's nothing theoretically 'wrong' with that.The worst I had was a radial with branches off left, right & centre but that was no biggie.
Amendment 2 allows this.or, in fact 1.0mm² cable if the regs allowed that for 'power circuits'