I thought the Icn value was the maximum value for the breaker but it may not remain servicable.
Ics - the in-service maximum capacity
Icu - I think comes from another standard?
I thought the Icn value was the maximum value for the breaker but it may not remain servicable.
Ics - the in-service maximum capacity
Icu - I think comes from another standard?
You should maybe have started a new thread.
The PSCC (prospective short circuit current) is the maximum available current which can flow in the event of a fault between live conductors, (phase-phase or phase-neutral) it is either directly measured or if your meter wont do direct phase-phase then phase-neutral doubled will suffice.
PEFC (prospective earth fault current) is the max fault current between a live conductor and earth. This can be measured directly or by dividing the max phase-earth supply voltage by Ze.
PFC (prospective fault current) is either the PSCC or PEFC - whichever is greater.