I'm talking about a MET which consists of an exposed earth block (rather than using a CU earth bar as the MET). It will usually be close to the CU (hence usually close to the meter and cutout). However, it's not unusual for gas and/or water services to enter in that vicinity, and quite common for gas meters to also be very close. Such a MET is therefore often in a general area where plumbers may well 'play'.I'm not 100% sure what you mean by an external MET? You only have one MET per installation. The MET is usually located by the electricity meter where plumbers don't play.
It would be, but that EICR might not take place until a good few years after the plumber had disconnected it.If it were that close then it would be obvious to any electrician that it had been disconnected during an EICR
If it were possible to get a cable/wire/whatever all the way through the old oil line (which I personally very much doubt), then it would presumably be possible to pull things through (e.g. small pieces of rag) and remove all but the slightest (and, I would say, irrelevant) residues of oil. I can't see that degredation of the insulaltion of the bonding conductor, even if it happened, would matter, and nor do I think that very slight traces of oil (after 'internal wiping') would be an issue in the (as you say, very rare) eventuality that the conductor getting extremely hot.I'd say no to using the oil pipe as a conduit as there may be residue in them. I don't know how heavy oil would react with it, nor how it would react to the cable becoming heated in a network fault scenario (albeit very rare).
Discussions in forums like this have a habit of taking on a life of their own. ... It's all very well having all this discussion about how best to loop bonding between gas and water services, but no-one has yet actually given us any reason to believe that the water service is actually bonded anywhere near where the gas service now needs bonding.I'd say join to the water MPB (main protective bonding) as stated on page 1 by lec //www.diynot.com/forums/electrics/query-from-the-combustion-chamber.371671/#2833052 My preferred choice anyway.
I don't think it did - at least, not clearly. As well as asking about the using the old oil line as a conduit, the OP also asked if the gas service could be bonded to the "already earthed mains water". EFLI replied that such would be fine, but I then pointed out that I had interpreted the question as relating to bonding to a water pipe (which itself was bonded elsewhere), rather than to extending the water service's bonding conductor.It said it was in the original post
I've got a job where their is a new gas meter & boiler going in at one end of a property & the electric incoming & consumer unit is at the other end. Customer does want floors up or really seeing the earth cable externally.
Their maybe a solution in their will be a redundant oil line under the ground floor screed, if at all possible to thread the earth cable through this pipe is this allowed or not? Probably not. Or earthing the gas to the already earthed mains water, pretty sure this isn't allowed.
Sparkies amongst us can one do either of these two options
Right. Thanks for clarifying. As you will have seen, 'linking a bonding conductor from the bonding clamp on one service to bond another service is allowed. Given the varying opinions about the best/acceptable way to do that, the method most likely to be acceptable to everyone would be to use a new continuous piece of cable to link the two clamps (on on gas, one on water) and to carry that new cable (again, 'continuously') and join it to the existing bonding cable (ideally with a crimped joint).It is generally accepted, as a gas fitter, that one cannot link a bond from a gas pipe to an existing bonding clamp on a water pipe, as we believe that the cable has to be a continuous length, and this is obviously not possible as a retro fit. Posts here seem to contradict that widely held belief, which s interesting in itself.
Ah, right. I misunderstood. I thought that second little paragraph was a response from someone, suggesting that there might be a redundant oil line which could be used as a conduit for a bonding conductor. I still think that's a theoretical possibilty (if one cleaned out the pipe first), but doubt you'd get the cable through it. We understood that the suggestion was to use the oil line as a conduit - the theoretical possibility of possibly using the oil line itself as a conductor was introduced (and essentially dismissed) by 'us' - sorry if that caused any confusion.The guy that posted this wanted to use the oil line as a conduit, rather than a bonding in itself.
That would not fulfil the purpose of main protective bonding, which is to connect the incoming service pipe to the electrical installation's Main Earthing Terminal (MET), to ensure that significant/dangerous voltage differences cannot exist between them.Another suggestion raised in the CC was to use an earth spike. This was generally seen as non conforming, buy IS it?
An earth spike is NOT the answer. The cable is a bond and NOT an earth. The purpose of a bond is to ensure all exposed metal work inside the building is at the same potential. This ensures anyone touching two bits of metal will not get a shock from them being at diffferent voltages.Another suggestion raised in the CC was to use an earth spike. This was generally seen as non conforming, buy IS it?.