An MCB will operate on overload (ie non-fault), also on short - circuit (L-N or L-E) The time taken to operate is inversely proportional to the overload/short-circuit current (usually 0.1 sec is taken as the fastest operating time due to mechanics for faults of negligible impedance)
An RCD operates quickly for smaller 'out of balance' currents ( ie the difference between L and N) So will most definately operate for a short - circuit between L and E and they usually operate for N to E faults depending on currents flowing in the installation.
The RCD is more sensitive and so is prone to nuisance tripping eg damp in fittings, poor insulation but is also there as additional protection as the small fault current could be flowing through you !
40mS is the required max. trip time for this kind of additional protection.
An RCD operates quickly for smaller 'out of balance' currents ( ie the difference between L and N) So will most definately operate for a short - circuit between L and E and they usually operate for N to E faults depending on currents flowing in the installation.
The RCD is more sensitive and so is prone to nuisance tripping eg damp in fittings, poor insulation but is also there as additional protection as the small fault current could be flowing through you !
40mS is the required max. trip time for this kind of additional protection.