no you can't get an RCD fitted as the main switch in the MG board as it would have to be a 3 phase RCD and I don't think they'll work on single phase..
you need to get that wylex RCD changed to a 100mA type S RCD.. ( time delayed.. )
adding a 50A RCBO to the MG board won't help one bit..
the 30mA main RCD will still trip before the 100mA one in the crabtree board..
i know i need to change the main RCD now as its 30ma, i guess this is wrong anyway?..to low mA..? can you get standalone RCDs these days? didnt think you could.
trouble is, the crabtree CU is still a 100ma so wont we still trip if there is a problem at the crabtree end.. so i was thinking, rather than try and get a lower rcd in the crabtree, (which will most likey go for days without being noticed) get a RCBO in the merlin so we can see when there is a problem.
so could i do both?