The 2nd test that I did today have changed things slightly. Before the boiler only used to fire for 1 1/2 minutes. It fired for alot longer today. The only thing that we have done what I think would have made a difference in the last couple of weeks since it was cycling is the bucket test and a new pump fitted - although alpha agent said this did not help. Possibly dislodged a slight block??
Test no. 1 - boiler at no. 7
Hot tap open a trickle so it does not fire boiler
Times below are the length of time the boiler fired for.
Boiler if off for approximately 3 minutes between each time it fires.
The temperatures below were checked on the pipes below the boiler.
1st fire = 24.24mins - F72, R41
2nd fire = 5.52mins
3rd fire = 5.20 mins - F72, R40.8
4th fire = 5.44 mins - flow and return did not change much from the above.
5th fire 5.50 mins - R40.5
Pump runs for approx. 20 seconds, then there is still some other noise coming from the boiler, is it a fan. During the 3 mins that the boiler is switched off, it still feels like water is moving around the pipes, is this normal?
All rads heated up well and too the bottom, except the big prob rad.
Test no. 2 - boiler at no. 7
No taps switched on
Times below are the times that the boiler fired, boiler off for approx. 3 mins between times below.
The temperatures below were checked on the pipes above the pump.
1st fire = 16.26min
after 7 mins firing, F73.9, R27
after 14 mins firing, F74.9, R38.4
after 16mins firing, R40.5
when boiler switched off, R41.5
2nd fire = 3.10 mins
Checked heat exchanger after this cycle turned off, measured 42.2 degs. Checked it also during other cycles and it stayed around this temperature.
3rd fire = 3 mins
4th fire = 3.10 mins
5th fire = 3.02 mins
6th fire = 3.15 mins
7th fire = approx. 2.50 mins (during this time on I went around and turned all rads back to only 1/4 turn on for the lockshields as Tony suggested. From this point forward, the only lockshield fully open is the problem rad and it DID NOT help. The rad did not heat up any further at the bottom, it is slightly hot, just off the cold)
8th fire = 2.55 mins
9th fire = 2.55 mins
I used a hannah instruments K-thermocouple thermometer to check the temperatures. It has been calibrated.
Forgot to say when I did the first test and had the tap slightly open, the water got boiling hot after the boiler was firing for a while on CH.
I told Alpha what I told yourselves about the diverter valve & they didn't believe me. When my boss spoke to them, they believed them. Could he be coming from the point that the diverter should stay fully over for CH and if the hot water is put on a trickle, hot water should not come out the tap. Therefore the diverter must not be closing fully for the CH and therefore it is passing for the hot water. My own basic thoughts but possibly doesn't work like this.
Hope this proves something. thanks