Hi All
We've a had a woodburner/heat store/neutraliser fitted and the gas boiler/DHW coil and CH all connect into the neutraliser.
It's all working fine and i'm doing some checks on efficiency. I noticed for some time that when the heat store is pumping and the gas boiler is off, the temperature on the on boiler display shows the heat store flow temperature!
Nice feature, you might think.
However, after running for a few hours on heat store, the airing cupboard is a bit like the tropics so this is wasted heat.
It turns out that with the gas boiler off, the top of it is very hot due to a reverse flow (thermosyphon??) from the neutraliser up the gas boiler flow and out of the return. I checked this by holding the gas boiler flow and return pipes and the flow gets hotter and more quickly than the return.
I'd like to stop this as heating the airing cupboard is not the reason I spend time cutting wood!
Would it be sensible to fit a check valve on the gas boiler flow?
Thanks
Steve
We've a had a woodburner/heat store/neutraliser fitted and the gas boiler/DHW coil and CH all connect into the neutraliser.
It's all working fine and i'm doing some checks on efficiency. I noticed for some time that when the heat store is pumping and the gas boiler is off, the temperature on the on boiler display shows the heat store flow temperature!
Nice feature, you might think.
However, after running for a few hours on heat store, the airing cupboard is a bit like the tropics so this is wasted heat.
It turns out that with the gas boiler off, the top of it is very hot due to a reverse flow (thermosyphon??) from the neutraliser up the gas boiler flow and out of the return. I checked this by holding the gas boiler flow and return pipes and the flow gets hotter and more quickly than the return.
I'd like to stop this as heating the airing cupboard is not the reason I spend time cutting wood!
Would it be sensible to fit a check valve on the gas boiler flow?
Thanks
Steve