No - hire professional electricians, like the one you are using, who don't know that ring finals are allowed and who then spur off more than one outlet using a cable which is too small, because they think it's a radial circuit.Don't hire cowboys that have no clue and randomly connect things without looking.
My question, and my verdict that your answer was completely wrong, was about my diagram, not your house.In the house in question, there was a "Spine" down the middle of the house from which all the outlets were sourced.
No - solution: You learn what you're talking about before whinging that something is wrong when it isn't.Additions had been made to this circuit. That's why I referred to them as "Spurs" off an original circuit.
Because I didn't use the correct terminology for your liking, you now have a stick up your rectum. Solution: Remove stick from rectum.
Well then I definitely don't know where you were coming from with this:In is 20A, As already stated in the previous two posts I've made.
"Imagine you create a single radial circuit, Let's say in your picture, from A to C, and use 2.5mm wire.
You plug in a Fridge at A, a TV at B and every now and a electric toaster at C.
Fridge at 200W, TV at 400W and electric toaster at 1500W. That's a total of 2100W.
The Distance from Consumer Unit to C is 25meters.
You decide to add a "Spur" from B to F which is 15meters , 2.5mm and plug in a 2KW heater.
You are now consuming 4100W over that same cable between the Consumer Unit and A. All still fine and well.
You decide to add another "Spur" from A to D which is 20M long, and powers a water pump for the garden periodically, which is 1500W.
You're on 5600W now, and exceeding the maximum current allowed for the leg between the Consumer Unit and A.
See where I'm coming from?"
because with a 20A breaker you're not going to be able to get to 5600W, are you.
You apply the worst one. Could be 13.5A, or even lower if there are other factors as well.Will be between 20A and 27A, I do not know exactly which figure to apply as there are various environments that the cable will run through (Ceiling with insulation, Conduit in rendered wall etc)
Then why have a ring?In any case, In ≤ Iz.
So you can't measure Ze on a TN-C supply?I have no idea what the value of Ze is as it currently is non existent.
Never knew that - you learn something new every day.
Don't you think you should have that info before you start deciding what size cables to use on what size protective devices?The maximum EFLI I do not know either, I do not know which type of fuses for consumer units are standard here, so I do not have any data sheets in order to calculate maximum EFLI.
Then the problem lies with the idiots, not the fundamental nature of a radial circuit, doesn't it.Try 3 or 4 idiots over a span of 50 years without any legislation covering it.
An idiot can **** up a circuit with just one outlet on it.
And introducing ring finals is going to give them new ways to **** up.
But we all know that.Well I don't know, something must be wrong with your head if you do not understand why I would mention that we do not have fuses on plug here like the UK does, after someone mentioned that 32A is permissible for a 2.5mm² ring circuit provided that fuses on plugs are fitted.....
When you go off to the wholesalers to buy your stuff you'll have to drive on the right.
By designing it such that Ib ≤ 20A, not by having the breaker trip when the current exceeds it.Ib is up to 20A
In is 20A
There for... Ib ≤ In
How else do you propose to limit the current in a circuit which you do not wish to exceed 20A?
Analyse this:Analyse the wording: OverCurrent Protection Device.
In dum dum speak: "Too Much Current Switchy Offy."
You wish to LIMIT the LOAD on a circuit to 20A.. Makes perfect sense to me, but apparently you have a different take on it, I'd love to hear it.
Your DESIGN current is supposed to be ≤ 20A.
You are talking though about limiting the load to 20A by having a protective device operate when it exceeds that figure.
Therefore you are talking about a DESIGN where you are limiting the load via the protective device, not a DESIGN where it's in it's nature for the load not to exceed 20A.
Therefore your design is flawed.
My apologies - I thought you'd already decided that 2.5mm² on a 20A breaker would be OK.By using the tables provided in the IEE 16th edition to compute it?
By finding out what type of fuses are standard here, and calculating the required EFLI. Then measuring to see if they are within limits?
And a 20A radial wouldn't work because....?Because the limiting factor is the 2.5mm2 wiring in ring, and it requires adequate protection. 20A is sufficient for a bedroom.
Then the fault lies with the numpty who added too much too it, not with the nature of a radial circuit.True,but the difference between radial and ring is the loading via two cables, giving two different paths to reach the same location.
The radial was never designed to have so much added onto it.
And if you introduce rings as a solution to the cables in radials not being up to it instead of using larger cables on radials then you will, 100% guaranteed, be worse off when the numpties start adding to it.
Result of adding too much new load to a radial circuit - OPD trips.Granted, the ring could have the same done to it, but its a lot more logical to me to have zones with rings than having a "loose end" somewhere you can tie into.
Result of adding too much new load to a ring when rings are not something you have ever heard of or encountered, and radials are all you've ever known - cables get damaged. Maybe a fire if you're really unlucky.