Ring Continuity Test

Yes, I think what we are saying is that it is comforting to find that R1 and Rn are substantially equal and R2 is substantially 1.67 times or whatever ratio is appropriate for the conductor size used, if all three readings fall pretty much in alignment it gives a confidence boost
 
Sponsored Links
Sometimes a "good" Earth continuity test can be masking a serious double fault in the CPC
Indeed - as I wrote early on ....
There's not really anything practical one can do about it, but one consequence of the issues being discussed above is that, in an existing installation, it is probably rarely, if ever, possible to be certain, by measurement, that the CPCs of the wiring are all intact and that the CPCs are all satisfactorily terminated.
There could be one or more breaks of the CPCs within cables (or their terminations) yet, if 'parallel paths' were present, one could get perfectly credible and reasonable 'continuity measurement' results.
However ....
If there is any doubt about the measured R of the CPC then a wander lead should be used to verify that each and every socket has an effective Earth
If one measures the resistance from every socket to 'an effective earth' (or, at least, the MET) then one will indeed be able to be confident that, at that point in time, there is an adequate (i.e. 'safe') connection to earth from each socket. HOWEVER, that does not in any way prove that the CPCs in the cable (and their connections) are intact, since the (currently) 'satisfactory' connections from sockets to earth might be via 'parallel paths' - which, at least in theory, might not necessarily be there for ever, something which might be of concern to a very risk-averse person.

Kind Regards, John
 
Whoops. I hope I`m not seen as a "Clever Cloggs" .....
So if I have offended John or anyone else then I am sorry, it was never my intention.
Goodness, I think you are being over-sensitive. I'm not very easily offended at the best of times, but I didn't even consider 'being offended' by anything you have written in this thread.

If it's any consolation, you are one of the last people here whom I would accuse of being a "Clever Cloggs" - I was thinking of those who have a very good knowledge of (and maybe 'worship') what all of the words in 'the regs' say (and don't say) but have a less impressive ability to think - like those who complain about 4mm unfused spurs from ring finals feeding multiple sockets.
.... I saw what I thought might be a typo and mentioned it to John (I have learned to respect John and his posts so much that I did a recheck on my calculator using 2.5 to 1.5 ratios just to remind myself).
...and I think exactly the same of you - and I am certainly (very!) capable of being guilty of typos, as well, sometimes, of true 'errors of thinking' (of facts) - so I'll never be offended by people questioning what I have written!

However, we have unearthed something a little odd. Goodness knows where all the sources (including BS 7671) get their figures from. but if a given manufacture were to publish figures indicating conductor resistances for a range of cable sizes which were not (exactly) inversely proportional to their alleged CSAs, that would surely indicate that some of their conductors did not have the intended CSAs.

Somewhat 'worse' than that, there are always going to be small manufacturing tolerances (in CSA), but one would expect/presume that the figures (for resistance) they published would relate to the nominal/'target'/typical/average/whatever CSA - so IF their resistance figures were not inversely proportional to CSA, that would seem to imply that they had 'deliberately' manufactured conductors with 'incorrect' (target/typical/whatever) CSAs.

The deviations from 'expected' we've been discussing are clearly not large enough to be of much practical consequence, but it would be interesting to know why they exist. As SUNRAY has pointed out, they cannot all be explained solely on the basis of rounding.

Kind Regards, John
 
It seems impossible to find a definitive value of a particular wire to start from.

Sites vary significantly in their figures.

This one comes up first on my search but as you can see very few of the values on the same site match.

Strangely, though, the 2.5:1.5 is spot on - but even the 1:10 isn't and both are higher than usual.

https://www.macartney.com/what-we-o...l-information/conductor-resistance-of-copper/

1692536782261.png
 
Sponsored Links
Well if someone asks you the time it is very rare that someone else will answer "its 27 minutes and 33 and a half seconds past ten in the morning".
Some might say 25 past 10, some might say half past 10, some might it`s between 10 and 11 and some might say it`s thursday morning or even just that it`s thursday. it depends on your need of accuracy in thar particular situation.

Actually, if you look at the published max and min allowed diameter for cable CSA you might be surprised how close some of it is consistently manufactured to with the last few microns of permitted sizes. Makes a bit of a mockery of allowing a manufacturing tolerance so relatively wide open. Of course the manufacturers aim to get away with the least amount of conductor allowable.
 
Last edited:
Well if someone asks you the time it is very rare that someone else will answer "its 27 minutes and 33 and a half seconds past ten in the morning".
Some might say 25 past 10, some might say half past 10, some might it`s between 10 and 11 and some might say it`s thursday morning or even just that it`s thursday. it depends on your need of accuracy in thar particular situation
They might but not very good if it is a quarter to two on a Tuesday.

How do you know which is wrong if you don't know which is correct?
 
They might but not very good if it is a quarter to two on a Tuesday.

How do you know which is wrong if you don't know which is correct?
Yes but how correct do you need to be to be considered not wrong?

"You are telling a lie!" . "Oh no I am not!" . "OK then if it`s not a lie then what is it?". "Well, it`s just a different version of the truth!" . Carla Lane , Bread, old "Electric Head" as we used to refer to him - The father of the Boswell Family - priceless comedy :giggle:
 
Depends if you are happy being slap-dash or not.

Do you make a habit of stating something slightly wrong when you know what is correct?
 
It seems impossible to find a definitive value of a particular wire to start from. Sites vary significantly in their figures. This one comes up first on my search but as you can see very few of the values on the same site match.
Indeed. It's very odd.
Strangely, though, the 2.5:1.5 is spot on - but even the 1:10 isn't and both are higher than usual.
Indeed. As I've said, I'm not so concerned about the absolute differences in figures in different sources (which could be due to all sorts of reasons), but one would expect the ratios of resistance to correspond with the ratio of CSAs to be the same for everything from a single source

As you say, the 2.5:1.5 resistance ratio from their figures is 'spot on', but that's not the case with any of the other pairs I've tried - and, at least in most cases, the discrepancies cannot be explained by rounding alone. For example, with the 1:10 (mm²) comparison you mention, the ratio of resistances is appreciably above 10 at both extremes of the possible rounding errors.

As for reasons for absolute differences, are the 'copper conductors' we talk about actually 100% pure copper?

Kind Regards, John
 
As for reasons for absolute differences, are the 'copper conductors' we talk about actually 100% pure copper?
no there is a target and an allowable tolerance too, just to beggar the pure arithmetic of the situation
 
Well if someone asks you the time it is very rare that someone else will answer "its 27 minutes and 33 and a half seconds past ten in the morning".
Some might say 25 past 10, some might say half past 10, some might it`s between 10 and 11 and some might say it`s thursday morning or even just that it`s thursday. it depends on your need of accuracy in thar particular situation.
Yes, but the number of significant figures in the figures they are quoting indicates the degree of precision ('accuracy') they are working for and, as I've just written, the discrepancy of 'resistance ratios' (in comparison with 'CSA ratios') we are seeing cannot be explained by the rounding alone.
Actually, if you look at the published max and min allowed diameter for cable CSA you might be surprised how close some of it is consistently manufactured to with the last few microns of permitted sizes. Makes a bit of a mockery of allowing a manufacturing tolerance so relatively wide open. Of course the manufacturers aim to get away with the least amount of conductor allowable.
Yes, but as I've also written, even give the existence of manufacturing tolerances (od CSA), no matter how wide, one would expect the quoted resistance figures to relate to the nominal/intended/typical/average/whatever CSA - so, again, should correspond with the raio of those CSA figures.

Kind Regards, John
 
no there is a target and an allowable tolerance too, just to beggar the pure arithmetic of the situation
As you presumably realised, my question was almost rhetorical, because there are rarely (if ever) cases of materials which are literally "100%" of anything - I imagine that even 'gold bars'/ingots have allowed tolerations of various 'contaminants.

If different people are making different assumptions about the composition of the 'copper', that could explain small absolute differences - but, again, that should not affect the 'resistance ratios' of conductors with different nominal CSAs.

Kind Regards, John
 
Let's see if I can work this out using the physics:

The resistivity (rho(Cu)) of pure copper is 1.68x10^-8 Ωm at 20C. The temperature coefficient is 4.04×10^-3/K, so corrected to 25C, rho=1.714x10^-8 Ωm ( a little higher as you would expect. BTW, Ωm is correct, it is not Ω/m)

The resistance of a conductor is given by R=rho*l/A, where l is the length in meters and A is the cross sectional area in m²

2.5mm² is 2.5x10^-6 m²

So the resistance per km at 25C of 2.5mm² copper is R = 1.714x10^-8 * 1000 / 2.5x10^-6 = 6.856Ω, This assumes pure Cu and DC but I would not expect significant reactive effects at 50Hz.

I wonder where the other values come from? Or am I missing something?
 
Last edited:
Well, (I am being extreme here though) lets say one department or one subcontractor is making all the L conductors, another the N conductors and yet another all the E conductors or even the same department etc but on different days of the week etc etc etc we might get subtle differences. There are many other ways to get subtle differences that might or might not explain some of them. I think most of us have heard the motor manufacturing term "Oh, it`s a Friday Car!".

No two things in the world are exactly the same so it`s a question of how far we need to move away from similarities to start to become significant for our particular application and that includes any theoretical figures we use too.
 
I'm not arguing - I don't know - but it seems relevant to the discussion:

The resistivity (rho(Cu)) of pure copper is 1.68x10^-8 Ωm at 20C.

This site:

says it is 1.77.
 