I recently altered a ring main which was inpsected and passed at the time but has now been rejected on a PIR.
It is about 10 double sockets around the stage area of a village hall fed by B32 RCBO approx 15m away. It had a contactor in both legs of the ring with one 3A SFCU 600mm in advance of a contactor. I have removed them and installed a single larger contactor, such that the two 2.5mm cables parallel feed power to the contactor and SFCU and the remainder of the ring forms the load.
The objection's are:-
1) I have formed a link across the ring.
2) Both legs of the ring need to come back separately to the CU.
3) It is untestable due to the way its wired.
My thoughts
1) The ring starts at the contactor.
2) Ditto
3) The standard ring tests can be performed, using the contactor as the start point.
4) The SFCU should not be connected where it is (it is the power source for the contactor control), the cable should be long enough to move this connexion into the contactor enclosure.
Although not impossible its impractical to replace cables between CU and stage area due to access into sealed voids. The circuit has been left disconnected by the tester to make it safe. They say it will need a new CU/CPD following the contactor to retain the ring or to change the ring section for a 4mm radial and retain the existing supply arrangement, they are aware the SFCU is there (they installed it originally).
All thoughts gratefully received, I don't have access till well into next week so by then I hope to have all the ideas I need.
It is about 10 double sockets around the stage area of a village hall fed by B32 RCBO approx 15m away. It had a contactor in both legs of the ring with one 3A SFCU 600mm in advance of a contactor. I have removed them and installed a single larger contactor, such that the two 2.5mm cables parallel feed power to the contactor and SFCU and the remainder of the ring forms the load.
The objection's are:-
1) I have formed a link across the ring.
2) Both legs of the ring need to come back separately to the CU.
3) It is untestable due to the way its wired.
My thoughts
1) The ring starts at the contactor.
2) Ditto
3) The standard ring tests can be performed, using the contactor as the start point.
4) The SFCU should not be connected where it is (it is the power source for the contactor control), the cable should be long enough to move this connexion into the contactor enclosure.
Although not impossible its impractical to replace cables between CU and stage area due to access into sealed voids. The circuit has been left disconnected by the tester to make it safe. They say it will need a new CU/CPD following the contactor to retain the ring or to change the ring section for a 4mm radial and retain the existing supply arrangement, they are aware the SFCU is there (they installed it originally).
All thoughts gratefully received, I don't have access till well into next week so by then I hope to have all the ideas I need.