It should not be used to carry a load of 32A.2.5 is rated somewhat lower than 32A therefore should not be on a 32A supply which I agree with!
Good words!
It should not be used to carry a load of 32A.2.5 is rated somewhat lower than 32A therefore should not be on a 32A supply which I agree with!
If they're a ring taken off another ring, then, yes.there are thousands of similar circuits in use across the land, are they all wrong?
A long time ago i used to do electrical work in a licenced theatre
Now I am just a householder
I would certainly have put a submain to the stage area, and I would probably have run it at inaccessible height, like the stage lighting supply and controls cables. With a small CU feeding your stage outlets, and if you want, some EPO buttons and a contactor at the stage end. I would have had the stage CU where it was visible and accessible to the stage manager for RCD and contactor resetting but not easily interfered with by others. You could take working lights off the stage CU as well.
If there was to be a ring, it would only start at the stage area. However I would probably not use a ring as I would not want sockets across the front of the stage. There would be no sockets taken off the submain. There would be no sockets in the stage area fed from other circuits.
BTW I would also have preferred different coloured, or identified, sockets on the stage circuit to reduce the risk of confusion with auditorium sockets when a circuit was isolated for maintenance.
If they're a ring taken off another ring, then, yes.there are thousands of similar circuits in use across the land, are they all wrong?
If you wanted to do it that way, you could have broken the old ring at two points and enlarged it into one big ring.
Or you could have had a 13A fused spur off the old ring with multiple outlets on it but this would be very limited.
Which regulation, i.e. xxx.y.z makes a 2.5mm² cable on a 32A breaker unacceptable?
433.1.1 The operating characteristics of a device protecting a conductor against overload shall satisfy the following conditions:
(i) The rated current or current setting of the protective device (In) is not less than the design current (Ib) of the circuit, and
(ii) the rated current or current setting of the protective device (In) does not exceed the lowest of the current carrying capacities (Iz) of any of the conductors of the circuit, and
(iii) the current (I2) causing effective operation of the protective device does not exceed 1.45 times the lowest of the current carrying capacities (Iz) of any of the conductors of the circuit.
If it was a 4or6mm instead of the parallel 2.5mm there would not be a question. Maybe a label informing of the parallel feed should rectify this.Is it a figure of 8, or is it a ring originating at a contactor which is supplied by a parallel circuit?
I think it could be described as fed at 2 points and a faulty contact out of 4 will result in one leg taking all the load, as opposed to to zero current if 1 out of 2 contacts fail.And anyway - I don't see anything wrong with a 4P contactor being used to break both legs of a ring. Are there actually any regulations against it?
No its not a reg, its an advisory appendixOr is there a regulation which says "Circuit designs which baffle hard-of-thinking numbnuts with no imagination or powers of original thought when they carry out PIRs shall not be used"?
So what's the situation with unfused 2.5mm² spurs from ring finals?it fails because in this instance In ( 32A ) > Iz ( 27A max clipped direct )
Is there the same concern, to the extent of saying "it could go wrong, so you mustn't use it", with 3- or 4-pole switches, contactors, MCBs, RCDs etc used in 3-phase circuits, where incomplete making/breaking of the circuit could cause problems?I think it could be described as fed at 2 points and a faulty contact out of 4 will result in one leg taking all the load, as opposed to to zero current if 1 out of 2 contacts fail.
To what extent should a designer be constrained by concerns over what incompetent and ignorant people, over whom he has no control, might do in the future?1: it's less bad (though still bad and there should IMO still be warnings) if some numpty puts sockets in the feed legs
So what's the situation with unfused 2.5mm² spurs from ring finals?it fails because in this instance In ( 32A ) > Iz ( 27A max clipped direct )