Is there the same concern, to the extent of saying "it could go wrong, so you mustn't use it", with 3- or 4-pole switches, contactors, MCBs, RCDs etc used in 3-phase circuits, where incomplete making/breaking of the circuit could cause problems?I think it could be described as fed at 2 points and a faulty contact out of 4 will result in one leg taking all the load, as opposed to to zero current if 1 out of 2 contacts fail.
No I'm not saying that at all and I don't think its fair to make the comparison.
Generally there is no increase in current when a phase fails in a 3ph system, if there is its most likely to be a motor circuit and will be protected by an overload device which will trip fairly quickly.
Back to the point in hand, lets assume (always silly) that the circuit is running at its full load of 32A and one contact of the 4 pole system fails, this means one wire is carrying the all the current.
The wire is running at around 120% of its capacity.
Now the real world, the circuit is 2.5mm singles in conduit and 75x50 trunking in insulation and I think its fair to guess its half full, lets say 10 circuits. I make it that the wire is running at around 333% of its capacity, unless I'm reading the (16th) tables wrong.