So when a 3-phase supply is described as "X volts", isn't X the phase to phase voltage?
Ah, I assumed you were using P-P as meaning peak-to-peak.
Actually, you go on to prove that you are still missing a fundamental concept.
Because the fundamental issue which has been concerning me is the supply. Yes, if you connect it star then the voltage across each winding is indeed 230V not 400V.
Eureka - now connect the dots ...
If each winding in a motor is designed for 230V then that motor can be used in delta on a 230V 3P supply, or in star on a 415V 3P supply as you go on to demonstrate :
But see my question above - what is the phase to phase voltage of the 3-phase supply used for the motor?
If a supply is described as 240V delta does that not mean a single-phase voltage of 139V?
NO, because a 3P supply is not STAR or DELTA, it is "just" THREE PHASE. It just has three line conductors providing sine wave voltages that are 120˚ apart - and may or may not have a neutral (some 3P systems are only 3 wires and no neutral). We'll ignore all those details as they aren't relevant - just concentrate on the 3 line connections.
Star and Delta have no meaning on the supply side - where they have meaning is in the connections for things like motors, transformers, and generators. But yes, if a supply is 240V 3P AND is a 4 wire supply with a neutral, then the neutral-phase voltage will be around 140V.
As an aside, I have worked on a true 220V 3P system. There was no neutral, 3P loads were just wired across the 3 phases, single phase loads were wired across 2 phases. This meant that all the single phase loads had two "hot" wires, and all the breakers were double pole. It was also a nominally a floating supply
The only "problem" which has concerned me is not how motors are wired, it is how there can be something called "230V 3-phase" for which motors are made. Unless, as I said, what's evolved is a mutually-supportive environment of 3-phase converters with a P-P voltage of 230V, and motors made to match.
That is down to you not understanding that a motor
winding is made for a specific voltage - and it's the arrangement of connections of those windings that gives the required supply voltage
for the motor. All 3 phase motors (at least of the sorts were talking about here) are inherently dual voltage - the voltage each winding is designed for (delta), and 1.7 times that (star).
Taking your diagram above. If the windings are each designed for 230V, then the star connected motor on the left will run just fine on a 415V 3P supply. If you try and connect it to the same supply connected in delta as on the right, then you'll be applying 415V to a winding designed for 230V - cue magnetic saturation, excessive currents, and if the motor doesn't have some suitable overload protection then it'll soon be an ex-motor, gone to meet it's maker, with burned out windings (if it hasn't set the place on fire first
)
But, since the windings are 230V, you CAN use the delta connection on the right to run it from a 230V 3P supply - as commonly found from low power 1P -> 3P inverters/variable speed drives.
If the windings were each designed for 415V, then it would only run properly on a 415V 3P supply if connected in delta as on the right - 415V across each winding. If you tried to run it in star, then each winding will have only 240V across it - there's be much lower magnetic flux, much less torque, will run slower for a given load, and probably counter-intuitively run hotter
But where this is useful is in starting large (especially high-inertia) loads. If you connect the motor in star initially and apply power, it will start turning with reduced torque and most importantly with significantly lower current draw. When it's already turning, disconnect the supply, quickly reconnect the windings in delta, and re-connect the supply - it'll then run up to full speed. This is "star delta starting" and is often used on large loads to reduce initial current and/or mechanical stress. There are automatic and manual devices for doing this (I had to scrap a perfectly good manual one clearing out dad's garage) that don't involve fiddling with the wiring
It's not suitable for all types of loads as it relies on the load not presenting full torque during startup. So great for things like fans and centrifugal pumps, high inertia loads like rolling mills (that can be unloaded for starting). What it can't help with is things like positive displacement pumps which reach full torque more or less in the first revolution (or less) unless hydraulically unloaded.
If there has been any mutual development, I think it'll have been in only two areas :
1) Using 230V windings instead of 415V.
2) Making all the connections available.
Going back some time, all decent manufacturers brought out the 6 winding ends to 6 terminals. When the "budget" manufacturers got into the race to the bottom of the pond, one way of shaving a few pence off the price is to leave out 3 of the terminals and hardwire the arrangement of windings - giving a single voltage motor.
Since there's a lot of uses for driving 3P motors from 230/240V single phase supplies, there's a market for 230/240V 3P motors. Thus an incentive for a manufacturer to spend the extra few pence needed to make the motor dual voltage - it'll still ship as a "415V 3P motor", but by moving links in the terminal box a user can use that same motor as a "230/240V 3P motor".