megawatt said:No competent installer would make such a mess of the soldering to have any negligable effect on flow IMO. If this is an issue for you, rather than opt for compression fittings opt for someone competent to do the work for you instead.
MW
I think that you have missed the point here. We often go to existing installations where we have no control over who did it or how it was done. In that case it often becomes obvious that the measured pressure drop is a lot more then the calculations give, sometimes 50-70%.
We are not in a position to open up the pipework to inspect it. Often we go to faults caused by lack of adequate gas pressure and find solder, jointing compound or PTFE tape blocking the joints.
Although it seems counter intuitive to me at the moment I will have to accept that a 22/28 has more resistance than a 28/22.
However could Sanj please suggest the possible resistance of a 22/28 compared with an elbow and the similar 28/22 transition to put this into perspective in the gas supply perspective.
I dont see a 1mB pressure drop in 21 mB as indicating a pipe coming close to its maximum flow capacity in a domestic situation.
Tony