You do not need other circuits on the load side of that RCD to witness this effect.
Maybe not, but in the scenario when the circuit on the other side of the FCU was still live and probably with loads my money is on a parallel path back to the tx
You do not need other circuits on the load side of that RCD to witness this effect.
You do not need other circuits on the load side of that RCD to witness this effect.
Maybe not, but in the scenario when the circuit on the other side of the FCU was still live and probably with loads my money is on a parallel path back to the tx
Am I going mad - no-one else touched anything, and the instantaneous trip at precisley the time I cut the cable implies the cable was live?
I can see your point but the energized circuits under load would slightly raise the Neutral potential with respect to earth because the Neutral would have some voltage drop across it. When you then short N-E on the load side of the RCD this causes additional current to flow from N-E but you do not need that additional current to trip the RCD.
You can do the following experiment:
On a TT or TN-S system:
1) Connect only a single circuit via one single RCD to the CU.
2) No other circuits connected at all.
3) Short N+E on the load side of the RCD will trip.
4) Now link (yes only for us professionals) the MET with N on the supply side. This is now limiting the N+E loop to inside the property.
5) Short N=E on the load side of the RCD. It will not trip.
What you are describing is a contrived situation that probably would not exist under normal conditions.
No it isn't. It is an experiment which confirms that you need no other influences within the property on any circuit to cause an RCD to trip when N is shorted to E. It rules out what you appear to say is required to trip the RCD. Though I accept what you say will help trip the RCD. It is very simple. Please try the experiment.
I don't see the point of raising having to switch off just the one circuit because other trades need power etc. I have to do that all the time and understand that. But that is not my point.
The RCD trips because there is a potential difference between neutral and earth on a TT and TN-S system.
When you short the N & E you create a situation where a small current flows in the Neutral side of the RCD and not in the Line side so the RCD sees an imbalance and trips. It will do that with other circuits on and drawing current and without other circuits on and not drawing current.
If you then link the Neutral and earth before the RCD then the RCD will not trip when you short Neutral and Earth on the load side. There is nothing contrived about this. It is plain science. I ask yo to try it before you reply. If you fail to get the same result than I will admit that you are right and I am wrong.
Yes, you will see the RCD trip on a TN-C-S system but when the short between N&E is distant from the electrical service entry point (the point where N&E are linked at the cut-out)
OK - when isolating the MCB, I will only get small currents in the way you describe .
thanks for drawing bernardgreen, it illustrates what I have been saying
what does this mean in a practicle sense from a safey point of view?
OK - I thought safe isolation simply meant opening the MCB for the circuit involved (after live/dead check, checking equipment etc). Since a neutral-earth fault on the dead circuit could still see current flowing from other circuits at the CU, what does this mean in a practicle sense from a safey point of view?
but the voltage between the earth and neutral wires would be very low. Less than 5 volts worse case.