Hello All
2.5mm ring is protected by a 32a rcbo in the main consumer unit.
I'm thinking about using a short length of 4mm to spur from a socket into the garage which is on the other side of the wall. This would feed a small "garage" consumer unit with a (I think pointless from a protection point of view) 40a or 63a main breaker switch. From there would be a single 2.5mm radial on a 16a mcb and another 1.5mm radial lighting on a 6a mcb.
Is that allowed or does the whole lot need to be on a 13a fused spur or does it all need to come direct from the main consumer unit ?
2.5mm ring is protected by a 32a rcbo in the main consumer unit.
I'm thinking about using a short length of 4mm to spur from a socket into the garage which is on the other side of the wall. This would feed a small "garage" consumer unit with a (I think pointless from a protection point of view) 40a or 63a main breaker switch. From there would be a single 2.5mm radial on a 16a mcb and another 1.5mm radial lighting on a 6a mcb.