You have it set (RANGE RATED) to 55% max which means that it's max output can't go higher than 55% of 40kw = 22kw, it may e vent be lower as the max output of that boiler may be 36kw to CH & 40kw to DHW.Does the boiler need to be running at 100% of it set maximum output, in my case 22kw for that flow rate calculation? The WB 8000 has a modulation ratio of 10:1, so does that mean in lowest tickover it's outputting about 2.5kw?
If so, using the calculation you supplied, would that then make my boilers current flow rate to be around 2.15 Lpm?
I hope I'm totally wrong though!
The WB 8000 has a modulation ratio of 10:1, so does that mean in lowest tickover it's outputting about 2.5kw?
Sorry to butt in, but I think earlier you said you now have it on CP3, and I think it was suggested to use CC3. Don't know if that would alter the calculation.The pump is actually an Alpha 1. It will only show power on the display, so I've been trying to make sense of this, but it's way beyond me.
I think our posts crossed. I think the pump might now be set to CP3, not CC3, according to a post a little while back. If that is right, it would seem to explain the discrepancy.This is your lefthand graph, above.
You will see power in W on the vertical axis, and the flowrate in m3.hr on the bottom horizontal axis, you know that the pump power is 28watts so draw a line horizontally to the right from 28 until it intercepts the Constant curve III, (your setting) then drop down vertically to the bottom horizontal axis and you will see that the flow is 0.41m3/hr = 6.83LPM, very poor for a pump that is running at a 6M head. Your flow rate should be at least 12LPM so problems?.
Well spotted Jonathan, this makes a huge difference, gives a flow rate of 0.95m3/hr, 15.9LPM @ 4.5M head on CP3, that's more like it and if correct, quite acceptable, CC3 should give ~ 15.98*sqroot (6/4.5) = 18.45LPM & ~ 35W so lets see.I think our posts crossed. I think the pump might now be set to CP3, not CC3, according to a post a little while back. If that is right, it would seem to explain the discrepancy.
"I ran it up to a steady flow temp of 64.5 where it's been sat for about an hour. All TRVS open with thr rads balanced to heat up about equally. Room temp is around 19-20. The boiler has modulated down to what sounds like minimum and the return temp is sitting around 48.8. The pump is running on CP3 as you recomended, 28 (watts?) on the screen."
Can you post a picture of your pump + the LED settings (present) so everyone is absolutely sure that the flow rate is as it now appears to be, perfectly satisfactory, and more so if on CC3.The pump is actually an Alpha 1. It will only show power on the display, so I've been trying to make sense of this, but it's way beyond me.