So a table which for each cable size tells you what its overall dimensions typically are, and what the diameter of each conductor is, makes no sense to you?I did locate the measuring guide in Wiki but to be frank, couldn't make head or tail of it.
No.would it be correct to say that the size of a cable can be roughly assessed by looking at it in cross section and measuring width times height to find the size in square millimetres?
Cable sizes refer to the csa of the L & N conductors, not the overall cable.
For cable you need to measure the diameter of a copper conductor...
You can use a ruler to measure the overall size, and then look up in the table what a cable with an overall size of x x y would be
You still seem to think that if a cable is stated to be, for example, 6mm², that that refers to any overall dimension. It doesn't - it refers to the csa of the L & N conductors, and they are not even slightly square..... even assuming you could find a section of cable where the corners were absolutely square.
It's up to you.So I'll go with my original thought and change this faulty shower for one of equal rating, in the sure and certain knowledge that the circuit will cope.
IMO it would make sense to find out the size of the cable you actually have, just in case the electrician who fitted a 32A breaker was an idiot.
Their recommendation is spot on. The breaker should have a rating ≥ the load. In this case the load of the shower (assuming they are quoting the performance at 240V) is 35.4A. You cannot get 35.4A breakers - the next size up after 32A is 40A.Shower manufacturers and their recommendations? Pfft.