Building Complexes with Interconnecting Services
Where there is one customer occupying several separate buildings on the same site, there will normally be only a single service for the whole site. The subservices from one building to another will be afforded by private cables. The ESQCR Regulation 8(4) prohibits customers from using CNE within their installations and ENA ER G12/3 section
4.9 gives guidance on the sizes of bonding conductor to be used. The required bonding sizes (copied as Table 2 in this CP) are related to the size of the incoming cable’s neutral conductor.
This is important in cases where a cable is laid between two separate buildings belonging to a customer on his own premises.
If there are incoming metallic services in a remote building which are separate from those in the building containing the Network PME connection, the bonding between the two buildings is related to the size of the incoming service, and not to the size of the cable linking the two buildings.
The reason for this is that the bonding might have to carry diverted neutral current following a fault on the Network.
It shall be pointed out that whilst the wire armouring of a PVC insulated cable may provide adequate capacity for short duration faults within the installation it will almost certainly be too small for equipotential bonding purposes.
In these cases then either a separate protective conductor sized in accordance with Table 2 shall be run, or, as a non-preferred option the cable shall be converted to CNE, and an ad-hoc approval sought