These pipes are 'bonded ' to the MET because they are 'extraneous' - they introduce earth potential.
If they become 'accidental' earth paths - so what - can't be avoided - the bonding is more important because, while everything is at the same potential (be it 50v or 230v) - you are safe.
Indeed. That's why I would want them bonded.
You seem like an intelligent fella, John, I don't know why you can't grasp this.
The issue is not about the difference between earthing and bonding. Hopefully we all understand the difference of concept and purpose, even if the two functions can sometimes be a bit difficult to separate.
The thing I can't grasp is the apparent inconsistency in what westie has told me - that if I have an earth rod for an outbuilding, with everything (including incoming supply pipes) bonded to that, I have to isolate that local earth system from the supply's earth, yet, if I disconnect the earth rod, I am then allowed (indeed, required) to bond the supply earth to everything in the building, including metal tubes or rods emerging from the ground, provided I promise not to call them earth electrodes. I obviously would
want to have the the e-p-cs bonded, for reasons we all understand only too well, but I just don't understand why I am allowed (per westie's COP) to do that (with a PME supply) when I'm apparently not allowed (per westie's COP) to connect the supply earth to something I choose to call an earth electrode.
In the case of TT'ng the outbuilding, the associated conductor CSAs are a lot smaller and will not satisfy the 'Regs' if the outbuilding also remains connected to the supplied 'PME' earth.
As above, what is confusing me is the apparent suggestion that it is acceptable to contect the 'PME' earth to the contents of outbuilding
and also to a metal object emerging from the ground,
so long as that metal object is called, say, a water pipe and not an 'earth electrode'. You also seem like an intelligent fella - can you not understand my difficulty with this suggestion?
Kind Regards, John.