Your allowed 3 meters from the origin to over current device if there are no branches, I am sure it is to allow from buzz bar to enclosure in a switch room, but it does not say that, so if you for example have 2 x 2.5mm² terminating into say for example a socket supplied from a 32A supply then you could have a single 2.5mm² from that point to say a FCU as long as it is unlikely to get damaged. 433.2.2 I am sure many of us have exceeded that 3 meters where the supply fuse is not a great deal greater than the cable capacity, although technically a spur from a ring main comes under that limit, cable rated at 22A with a MCB at 32A it is unlikely if the cable damaged that the 32A MCB would not trip, as long of course that the loop impedance is low enough, however that is not the case with 300A buzz bars and a 6mm supply to a lighting distribution board. However there is nothing in the regulation which says this. So in theory an unfused spur from a ring, or a garage consumer unit fed to 6mm² from the 100A incoming DNO fuse would both be limited to 3 meters, even when we know with the 13A socket or with at 32A and 6A MCB it is very unlikely the cable will be over loaded other than through damage to the cable in which case as long as the loop impedance is within limits the protection device will open.Which 3m limit is that?
However today it does not seem to matter about common sense, if the regulations are breached then you may find it listed on an EICR, I remember one where the builder to finish the house had a load of 500W halogen lamps to dry off plaster, the cables went through door ways and some electrician had followed the Best Practice Guide and failed it. By time I arrived the builder had finished and taken all the lamps away, so there was nothing wrong with in installation, in fact there never had been, to me if your checking the installation then multi-adaptors plugged in as shown in Best Practice Guide are beyond your remit. OK unplug them, but to list as a failure is wrong.
However how do you work with common sense if the person is not trained, it may seem plain to us, but would it be plain to the first year apprentice? I have seen where some one has allowed something to happen as in that situation it was reasonable safe, but then the same thing has been repeated where it was not, and it's too easy when the installation is not in front of one to say yes that's OK but some has been missed. So I suppose for the forum one has to be super careful, we will get some one who will say "I checked on a forum and they said it was OK" when they have missed out something vital.