Then you agree with me ....
Are you saying that you agree with me that, whilst (given the 'caveat') what you suggested would, strictly speaking, be compliant with regs, virtually no-one would ever do it?
.... so how can the regulation apply to the spur?
... I don't really understand the connection. 'The regulation' essentially exists to over-ride others in certain circumstances, so I can't see that one can make any assumptions such as you have done.
Is it not the case that very often the fuse in a plug is not really necessary?
I don't know if it is 'very often', but the fuse is theoretically unnecessary IF (and only IF) the load is not considered likely to cause an overload - since the cables connected to plugs would very rarely (if ever) have a CCC of 20A, let alone 32A.
Why then does it say "with or without unfused spurs"? Does that not signify that the spur has nothing to do with the ring regulation?
As I keep saying, that can be read either way - yours is one interpretation, the alternative is that the entire of the paragraph which follows (with is prohibition of <2.5mm² and <20A) applies to both the ring and any spurs from it. Given the total (logical) inexplicability (at least, to me, of the 2.5mm² minimum) I wouldn't dare to even guess what the intended meaning of the reg is/was!
The 1.5mm² would not be allowed anyway if the installation method prevented it so how can that be the reason for its prohibition?
As above, goodness only knows why 1.5mm is not allowed, at least in the ring itself, if not also spurs.
For what it's worth, the diagram ('guidance') in Appendix 15 shows an FCU spurred from the ring with 2.5mm² cable. Since 1.5mm² would clearly suffice (electrically), that might possibly suggest that (for whatever reason) the "2.5mm²/20A minimum"
is meant to apply to spurs, as well as the ring, mightn't it?
Well, we are talking about you thinking that is what it might mean when clearly there are instances where it does not.
I don't think that "clearly" and the reg in question can be spoken of in the same breath!
Kind Regards, John