Thanks. That's obviously what Harry and myself are both "vaguely recalling" !I don't have it with me (I'm away), but I remember in the 14th Ed., something like you could have two single sockets or one double on an unfused spur.
Kind Regards,John
Thanks. That's obviously what Harry and myself are both "vaguely recalling" !I don't have it with me (I'm away), but I remember in the 14th Ed., something like you could have two single sockets or one double on an unfused spur.
I know this is a no but from a 16A breaker in my CU, I have a 2.5 single feed to my garage at home. That goes to a double socket. From that socket there is a feed to another double socket also in the garage, a spur for the garage lights and security light and a feed to another double socket in the shed that runs a small freezer and a tumble drier as well as another spur for the shed lighting. Been like that for at least 10 years. Never had a problem.I've just had a thought. The double socket is either an end radial or potentially a spur off. (only L,N & E at rear of this socket), How can I tell if this is a spur off somewhere else or end radial? If it's a spur off somewhere else this would obviously mean my new single socket spur off might be off a spur which is a NO!
Nonsense. Stop perpetuating these silly myths.... which can serve a floor area of not more than 50m².
I’m sure I’ve mentioned it on here before and been told it was a no no. Is it okay?Why do you think that is a no?
I know this is a no but from a 16A breaker in my CU, I have a 2.5 single feed to my garage at home. That goes to a double socket. From that socket there is a feed to another double socket also in the garage, a spur for the garage lights and security light and a feed to another double socket in the shed that runs a small freezer and a tumble drier as well as another spur for the shed lighting. Been like that for at least 10 years. Never had a problem.
I’m sure I’ve mentioned it on here before and been told it was a no no. Is it okay?
Another incidence of 'guidance' being cited as if it were regulations.What you have is a 16A (or, more usually 20A) radial circuit which can serve a floor area of not more than 50m²....
Another incidence of 'guidance' being cited as if it were regulations.
I don't know about 'ancient history (you're the expert on that!!)', but there has certainly not been ny such regulation in the last few editions of BS7671.
Quite so - and there is little common sense in a 'guideline' such as the one secure mentioned.Sometimes, you have to just engage common sense, with regard to an installation, or a circuit - in normal use, is the circuit liable to overload, or tripping the MCB. Mottie hasn't reported even the 16amp as tripping, so the proof of the pudding....
I think that strictly speaking that is guidance - it is a good idea to follow guidance in most circumstances because it is usually put there for good reason, if you choose not to follow it then by using sound engineering judgement then I would be ok with that, but if you have not got the combination the competence by virtue of qualifications and experience then it is more sensible to follow the guidance. Guidance is there for a reason and whilst it does not cover every case it is often basically a set of simplified rules it is expected in most cases to achieve the objective goal of trouble free and safe installations.What you have is a 16A (or, more usually 20A) radial circuit which can serve a floor area of not more than 50m²
The problem is that unless the guidance is so 'conservative' ('ultra-cautious') as to be almost 'fool/idiot-proof) (which will often make it 'unrealistic'), it really relies upon those who may apply it to have the skill and knowledge to know when it is appropriate guidance (in which casethey probably would not need the 'guidance', anyway!)_I think that strictly speaking that is guidance - it is a good idea to follow guidance in most circumstances because it is usually put there for good reason,