If the socket is already a spur, the FCU would make no difference - so no point having an FCU.If in doubt there's no harm in coming off the socket via an FCU even if it is just for a TV.
If the socket is already a spur, the FCU would make no difference - so no point having an FCU.If in doubt there's no harm in coming off the socket via an FCU even if it is just for a TV.
Could I run the cable straight from the back of the socket to the FCU? Then from there to my new socket behind the TV?
If the socket is already a spur, the FCU would make no difference - so no point having an FCU.
It will be "fused down" by the fuse in the plug - an FCU 'protecting' a socket off a spur will do nothing to help.I do agree, but without reading back through the posts I don't think we don't know if the socket in question is already fused down or not. In which case I would be happier knowing that the extended socket is fused even if it is just powering a TV.
It will be "fused down" by the fuse in the plug - an FCU 'protecting' a socket off a spur will do nothing to help.
The plan is to have 2 double sockets behind the TV. All that will be there is a TV, sky box, and a soundbar. The socket that will be the “donor” is in the corner and all that will ever be in that is a lamp.
Draw the circuit.
Yes, so what good will an FCU between socket 1 and 2 do?A bit basic, but you get the idea.
Yes, so what good will an FCU between socket 1 and 2 do?
...but that still would not limit the load before socket 1. The cable after socket 1 is not the problem.Depends on if we're assuming socket 2 is a single or double.
Nothing in the case of it being a single. Like you said, the fuse in the plug would limit the load after socket 1 to no greater than 13A, so no different to using an FCU.
Exactly.Obviously nothing stopping us reaching 26A on a double though. The issue there being the current passing through the cable to socket 1, especially if running something from there too.
Aren't both sockets - either side of chimney - both likely to be on a ring circuit?In an ideal world though it would be good to know if socket 1 is running off an FCU to protect the cable feeding it.
Well, assuming the sockets, from which the spur is to be run, are on a ring, then I would use 4mm² for the spur which could then have as many sockets on it as you like.I'm interested in your thoughts though as I am known for overkill use of protective devices.