Many thanks to all who have taken the trouble to reply!
I'll put my hands up to the criticism - I have done the job all back to front.
In my defence, I was under some pressure to get the cable laid so that the trench could be backfilled. It was blocking access to the site.
Still I am where I am now and piecing together all of your advice, I don't think it is a complete disaster.
1. John is [probably] correct in saying that the load won't draw anything like 80A or even 63A. That said, given that the cable is there, I might as well protect it using the highest rated protective device possible.
2. I understood the maximum rating of the cable is what it can carry under test conditions in a lab. In any real life installation, this depends on the ability of the cable to dissipate heat which will be much less, for example, when it is ducted underground.
3. To answer RF Lighting and Lectricians question, I checked the Voltage Drop using TLC's online calculator. It recommended a minimum 16mm 3C cable for a 15kW load. Checking this again, it gives a VD of 2.1% at 65.2A with a maximum cable load of 66.8A.
4. Whilst limiting the load to 50A may ensure that the voltage drop is allowable, it is easy to conceive of the studio requiring more than this. As the load increases, I would rather be warned by the lights dimming than by the protective device tripping - assuming of course that the cable isn't smoking at the same time!!
So, how about this for the sub-main with the existing cable:
Garage/supply end: 80A MCCB
Studio end: 63A RCBO 30mA
As ever, your thoughts and advice would be much appreciated.
Regards,
J
I'll put my hands up to the criticism - I have done the job all back to front.
In my defence, I was under some pressure to get the cable laid so that the trench could be backfilled. It was blocking access to the site.
Still I am where I am now and piecing together all of your advice, I don't think it is a complete disaster.
1. John is [probably] correct in saying that the load won't draw anything like 80A or even 63A. That said, given that the cable is there, I might as well protect it using the highest rated protective device possible.
2. I understood the maximum rating of the cable is what it can carry under test conditions in a lab. In any real life installation, this depends on the ability of the cable to dissipate heat which will be much less, for example, when it is ducted underground.
3. To answer RF Lighting and Lectricians question, I checked the Voltage Drop using TLC's online calculator. It recommended a minimum 16mm 3C cable for a 15kW load. Checking this again, it gives a VD of 2.1% at 65.2A with a maximum cable load of 66.8A.
4. Whilst limiting the load to 50A may ensure that the voltage drop is allowable, it is easy to conceive of the studio requiring more than this. As the load increases, I would rather be warned by the lights dimming than by the protective device tripping - assuming of course that the cable isn't smoking at the same time!!
So, how about this for the sub-main with the existing cable:
Garage/supply end: 80A MCCB
Studio end: 63A RCBO 30mA
As ever, your thoughts and advice would be much appreciated.
Regards,
J