I know that terminating that SWA in the KMF will be a real pig! but hey ..
Fair enough.Thanks John, I think I'm sold on that 80A KMF switch fuse at the supply end and a DP 63A MCB at the studio end.
You can't do that. You need to terminate the SWA into some sort of box and then take 16mm² double-insulated singles from there into the switch-fuse.I know that terminating that SWA in the KMF will be a real pig!
It's not quite as simple as that with the KMF, since you need to separate out the conductors for separate entry into the KMF. However, it's not that difficult to find a way of doing it.
They do. In fact, the issue often is in finding one which isn't metal!They make switch fuses in metal clad these days.
You could well be right. Furthermore, the forum police must be asleep or distracted, since I've yet to see any mention of electricians, the signing of declarations on certificates or of notification of a job which will inevitably involve the installation of 'new circuit(s)'The more I'm reading here the more I get the feeling the OP is well out of his depth with this job.
True. I suppose it's my fault for mentioning the KMF, which i did because the OP seemed concerned about size. Mind you, I make no apologies for advocating a switch-fuse, rather than attempting to originate this substantial sub-main from a CU (even if that did mean a KMF plus another box!)!The KMF is for tails, or T&E/split con with the additional clip on shroud. Wouldn't go near one with SWA.
is really a 100A supply or just one which happens to have a fuse carrier marked with 100A.I have a 100A PME supply to a garage
Even if the garage really is a 100A supply, 80A being used for a submain leaves very little for the existing circuits.The SWA cable has a maximum rating of 91A and I designed the installation on this basis. I realise now that the cable won't be able to take this load in practice and I think I will have to downgrade the design load from 80A to say 63A.
Yes, like this (slit between holes if someone asks).It's not quite as simple as that with the KMF, since you need to separate out the conductors for separate entry into the KMF.
This doesn't seem the right way round. You calculate the load and then the minimum size for the protective device. This is used to calculate the size of the cable. As for the thread, if the OP is an electrician, he is out of his depth.Quite apart from the (probably limiting) issue of voltage drop to which RF has referred, in design terms you appear to be approaching this issue somewhat 'back-to-front'. The 'design load/current' should be the actual required load (or, at least, an estimate thereof). The cable is then required to have a CCC at least as great as that design load, and, in turn, the device protecting that cable has to have an In no higher than that CCC.
Kind Regards, John