Hi all,
Thanks for taking the time.
I'm looking to supply power to a shed/workshop I've just built a few metres from the house, and from there down a 25m run to a small BBQ cabin.
So I've had an electrician out to quote for the job this morning left concerned that the supply was not earthed sufficiently/at all. I believe I have a TT system, perhaps someone could confirm (if that's possible from just a picture?).
The electrician wanted to confirm earth as none is visible from the front as you can see. He removed the front of the CU and the first earth cable on the earth bar is large gauge 16mm2, great, we've found the main earth bond cable. He's cut the supply, removed this 16mm2 cable, setup his Fluke MFT, connected one cable to this and then one to the main switch live and it's come back with a reading of exactly 200ohm, which I now understand to be the loop test Ze result. He confirmed the connection at the earth cable and tested again, again 200ohm.
He then tested the next cable along, a 6mm2 and that gave a reading of 30ohm, we believe that to be the bonding to the gas meter and mains water pipes.
Essentially he's now advised that he cannot carry out any work until this is addressed as effectively the supply is not earthed & that reading is effectively open circuit.
Now, the property underwent a full re-wire and renovation including an extension about 5 years ago (before we bought it) the CU is a new metal type and all the wiring, including this 16mm2 earth all looks new, I just find it hard to understand how this could be so serious after going through a full re-wire quite recently.
I've been doing a little reading and from what I can tell 200ohm is the limit of what is acceptable, not ideal but still acceptable and not in line with the advice that the house is unearthed and actually dangerous.
Can someone verify? Thanks!
Thanks for taking the time.
I'm looking to supply power to a shed/workshop I've just built a few metres from the house, and from there down a 25m run to a small BBQ cabin.
So I've had an electrician out to quote for the job this morning left concerned that the supply was not earthed sufficiently/at all. I believe I have a TT system, perhaps someone could confirm (if that's possible from just a picture?).
The electrician wanted to confirm earth as none is visible from the front as you can see. He removed the front of the CU and the first earth cable on the earth bar is large gauge 16mm2, great, we've found the main earth bond cable. He's cut the supply, removed this 16mm2 cable, setup his Fluke MFT, connected one cable to this and then one to the main switch live and it's come back with a reading of exactly 200ohm, which I now understand to be the loop test Ze result. He confirmed the connection at the earth cable and tested again, again 200ohm.
He then tested the next cable along, a 6mm2 and that gave a reading of 30ohm, we believe that to be the bonding to the gas meter and mains water pipes.
Essentially he's now advised that he cannot carry out any work until this is addressed as effectively the supply is not earthed & that reading is effectively open circuit.
Now, the property underwent a full re-wire and renovation including an extension about 5 years ago (before we bought it) the CU is a new metal type and all the wiring, including this 16mm2 earth all looks new, I just find it hard to understand how this could be so serious after going through a full re-wire quite recently.
I've been doing a little reading and from what I can tell 200ohm is the limit of what is acceptable, not ideal but still acceptable and not in line with the advice that the house is unearthed and actually dangerous.
Can someone verify? Thanks!