Hi John, Thanks for the response. Yes the 2.5 is supplying the single socket, I know it's 2.5 as I opened it to have a look. As for whether it's acceptable I would submit to your better judgement?
Having 2.5mm cable supplying one socket is not, per se, a problem - the potential issue is having it protected by a 32A MCB. Provided the cable is not too long, I would probably be happy - but others may disagree!
...The problem I have is that there is very little space available in the conduit space (running through dining room, kitchen and bath room) to easily run cable out to the external wall (diameter wise) so swa may be too thick to do so. ... I am wondering if I (or my electrician) can run twin and earth to a more convenient junction inside the house, then from that junction to the shed in swa?
There is no reason why the indoor bits have to be SWA - so, if it would help,it would be perfectly acceptable to have the initial (indoor) part of the run in 6mm² (or maybe 4mm²) T&E, before changing to SWA at some box (or accessory) - as I said, maybe making the join at the present socket. As I said, I'm sure your electrician will have views on what approach should be taken.
Kind Regards, John