I wonder, however, whether having 26A worth of downstream BS1362 fuses is considered to render it "unlikely that the cable could carry overload current", given that the fuse(s) would obviously allow more than 27A to be carried indefinitely, and much higher currents for appreciable periods of time?
No more than an unfused <3m spur.
Yes, but the matter of unfused spurs (from ring finals) is totally different, regs-wise, from what is being discussed in this thread. The concept of unfused spurs from ring finals, for which cable with a CCC as low as 20A is allowed to be protected by a 32A OPD, is simply 'allowed' by the regs (aided by App 15),
without any need to invoke 433.2.2 (to justify the situation on the basis of downstream overload protection) or 433.3.1(ii) (to justify it on the basis that overload protection is not required, no matter what the length of the spur (I think - I'm not aware of any restriction in the regs).
On the other hand, if you want to invoke (in a situation which is
not that of a spur from a ring final) 433.3.1(ii) in order to allow a >3m cable (of inadequate CCC in relation to the upstream OPD), on the basis that overload protection is not required (at all), then the designer has to be satisfied that "the characteristics of the load or supply are such that the cable is not likely to carry overload current". Hence, as I asked, is 26A worth of BS1362s necessarily enough to satisfy the designer that, say, the CCC of 2.5mm² cable (at best 27A) is 'unlikely' to be exceeded? I really don't know what they intend here.
With a single socket, there would presumably be no concern.
So, you agree that the 3m rule can be overcome by this principal.
Probably yes - but in this case I would say that it's pretty reasonable to invoke 433.3.1(ii), since is is surely 'unlikley' that one will get more than 27A through a 13A fuse for a significant period of time? As above, it's rather different with 2 x 13A fuses.
Kind Regards, John