Am I correct thinking this is a 1500W pump?
Any contactor with an AC3 rating of 6A will be fine. If this is commercial any motor over 370W should be correctly protected with an appropriate overload
View attachment 321998
Which fits directly on the side of the contactor (excuse the mixing of makes which should not be done in actual use.
View attachment 322002 and all 3 passes through the overload must be used in order for the thermal element of the device to respond correctly.
Another variation goes before the contactor and acts as an MCB but still requires 3 passes of the load current.
View attachment 321999
Personally I'd fit either one regardless of whether it is commercial use as the pump is left unattended for automatic starting.
In reality the contact rods will be working at a much lower voltage than the supply, IIRC the rule is something like 6V or so. I wouldn't be worried about running it on 230V.
If you do use 24Vac for relay and contactor, do get a
control transformer rather than SMPS for reliability.