It's a problem with TN-C-S in general, it can easilly cause significant currents in things that were never really meant to carry signficant currents be they water and gas pipes or the lead sheaths of former TN-S cables.
It's not usually too much of a problem because things with low CSA also have relatively high resistance so in most cases will only get a small share of the current. Larger CSA items will get more current but will also be better able to deal with it. The exception to this is when you have a long section of large CSA metal and a short section of small CSA metal.
That is why we have sizing requirements for main bonding conductors in TN-C-S systems.
You say that cable is carrying about 1/3 to 1/2 of the instalaltions neutral current. Even without harmonic loads in a worst case loading scenario the neutral current could be as high as 400A before the phases are overloaded making the earth current betwen 133A and 200A. Harmonic loads could make things worse still.
IMO you really need to call them back and tell them that you belive the conductor sizes they have used in the PME conversion are too small.
It's not usually too much of a problem because things with low CSA also have relatively high resistance so in most cases will only get a small share of the current. Larger CSA items will get more current but will also be better able to deal with it. The exception to this is when you have a long section of large CSA metal and a short section of small CSA metal.
That is why we have sizing requirements for main bonding conductors in TN-C-S systems.
You say that cable is carrying about 1/3 to 1/2 of the instalaltions neutral current. Even without harmonic loads in a worst case loading scenario the neutral current could be as high as 400A before the phases are overloaded making the earth current betwen 133A and 200A. Harmonic loads could make things worse still.
IMO you really need to call them back and tell them that you belive the conductor sizes they have used in the PME conversion are too small.