And so doesn't comply, even without considering the final circuits...
If you mean the 25mm², then yes - but I, for one (and perhaps also you, judging by the strength of your previous comment) was more than a little surprised by how close it got. Once the OP has determined what the real design current is, I rather suspect that 25mm² will prove to be more than adequate.And so doesn't comply, even without considering the final circuits...
Well, that's the thing, isn't it.I had assumed that he meant what he wrote - i.e. 3 x 32A 3-phase (i.e. 'red') sockets - hence 96A per phase when fully loaded.
Obviously an important question - but wouldn't the latter be a very unusual way to be specifying a 3-phase supply? Having said that, as you've already observed, it's very odd that we're being asked the question, anyway - so I guess that 'unusual terminolgy' would not be impossible. As you have observed, if the designer cannot even work out cables sizes, he shouldn't be designing.Well, that's the thing, isn't it. Does "100A" mean 100A per phase, or 100 "three-phase" amps?I had assumed that he meant what he wrote - i.e. 3 x 32A 3-phase (i.e. 'red') sockets - hence 96A per phase when fully loaded.
I don't know what the usual terminology is.as you've already observed, it's very odd that we're being asked the question, anyway - so I guess that 'unusual terminolgy' would not be impossible.
Well it seems as if he can't. and therefore it seems as if he shouldn't, but perception can be flawed, and what I actually asked was 'Why has he taken it upon himself to design "the following" when he isn't able to work out cable sizes?'.As you have observed, if the designer cannot even work out cables sizes, he shouldn't be designing.
Maybe it varies. FWIW, it is very clearly documented that what I have here is a "3-phase 80A supply", and equally clear that what I have is 80A per phase.I don't know what the usual terminology is.
If you mean the 25mm², then yes - but I, for one (and perhaps also you, judging by the strength of your previous comment) was more than a little surprised by how close it got. Once the OP has determined what the real design current is, I rather suspect that 25mm² will prove to be more than adequate.And so doesn't comply, even without considering the final circuits...
Kind Regards, John
People seem to pluck figures out of the air and then ask for a cable size. Quite often they are rediculously high figures based on the incomer of a fuseboard or something, with no account for the actual anticipated current and future loading.
As I said, in my world as well, but BAS's comments made me wonder whether there were some who used terminology differently. As I implied, it certainly would seem very odd (and, I would have thought very confusing) to me to describe as "TP 100A" a supply which was 33.3A per phase!In our world if you require a TP 100A supply then that is 100A per phase.
That's what I'd always thought. Thanks for confirming.If you talk in amps, it's usually per phase - A 63amp TP submain would be 63amp per phase. If you talk in KVA, it's usually total. A 55KVA supply being 3 x 80amps.
Quite so. As I said, I suspect that once the actual current requirements are known, a relatively 'modest' (maybe 25mm², maybe even smaller) cable may well suffice.People seem to pluck figures out of the air and then ask for a cable size. Quite often they are rediculously high figures based on the incomer of a fuseboard or something, with no account for the actual anticipated current and future loading.
Exactly. As above, that was also very very point. My initial instinct/gut feeling was also that 25mm² was 'way out of court' - which is why I was a little surprised when I did the sums and discovered how relatively 'close' it actually was.My initial comments were based on instinct, not being near a regs book or calcing software. ... 25mm is taking the p**s.If you mean the 25mm², then yes - but I, for one (and perhaps also you, judging by the strength of your previous comment) was more than a little surprised by how close it got.
Quite so, and as I said:35mm is pushing your luck (doesn't comply for lighting, just about does for non lighting). ... Neither takes into account final circuits, which in a barn, are often long in themselves. ... A 50mm would do nicely for short final circuits, and no further submains after it. a 70mm would be ideal. ... You need to know the EXACT length and an accurate PROPOSED loading to work it out accurately.
Once the OP has determined what the real design current is, I rather suspect that 25mm² will prove to be more than adequate.
People seem to pluck figures out of the air and then ask for a cable size. Quite often they are rediculously high figures based on the incomer of a fuseboard or something, with no account for the actual anticipated current and future loading.
Okay, I have came to some sort of sense of his thinking, "Lectrician" what you said seems the obvious here so Im going on the basis that he genuinely didnt know what amp rating he needed,
Im thinking hes either done one of the following,
32amp socket x 3 phases = 96amp, making him want cable rating 100amp (wrong)
or
have 3 x 32amp sockets = 96amp, where he must have not though to consider diversity (i think is the word?), I am pretty sure he will NOT use 100amp constant at any point on the planet,
Please disregard all previous said,
what size and type of cable for 100m buried (copper or aluminum core) for the supply of 1 x 32amp and 1 x 16amp three phase sockets, (or does anyone know a good calculator)
Thanks
Thinking alound .... As I see it, the situation with lighting can actually be a bit 'worse' than one might at first think, unless one is able to balance the lighting loads across the 3 phases.If you need lighting too, then it is still 35mm (50mm Alu), as 25mm drops just a couple volts too much for the 3% drop allowed for lighting.