Then you might not get discrimination with the sockets - the 16A MCB might not trip before the 13A fuse at the house end blows, and you won't achieve your design goal of the convenience of separate MCB's and not having to to fiddle about behind the kitchen units.
Btw, excluding the c/u, how much to install a new 6 way in the
house,do you reckon?
Depends on so many things - you need get a number of quotes. And you should probably be thinking in terms of a bigger board than that - a 14 or 16-way split load. Sounds huge, but that actually gives you 10 or 12 circuits. Do a search here for topics relating to split load and you'll see how quickly they get used up....
That's news to me, as I always thought the 32a MCB was specially designed to discriminate correctly with a 13amp plug fuse, after all it's the mainstay of domestic power distribution in a modern home.
So, i should use a 6a for the light circuit and a ? for
the sockets.
Also, i was always lead to believe not to spur from a spur,
is this not what i'm about to do?
but i have heared of people cutting through flex (two core so no effect on rcd) with theier hedge trimmer and it taking out the mcb and not the plug fuse
the trouble is that if you hit the mag trip on a mcb it trips insanely fast before anything has happened to the fuse