Hi Mark.Yes it's a domestic kitchen there is already a dedicated circuit with 6mm cable going from 32mcb to 45cooker switch then 45a cooker connection plate then 6mm cable to cooker. But we are getting a smaller single oven which is only 16amp but need be hardwired. So should I change 32mcb to 16mcb I'm consumer unit or just get electrician to wire it straight into connection plate with cable supplied.
Please be aware winston1 is renowned for giving incorrect and sometimes unsafe advice.
Does the new new oven come with a flexible cable attatched?
The 'official circuit design criteria in the regulations' is all about protecting the electrical installation. ie; primarily to protect the cable and switches against overloads.
On that basis if the oven has terminals for a cable to be connected to and you are able to use the existing 6mm² cable, then the MCB may be left at 32A.
If the oven has a flex attatched which is then terminated in the wall connexion plate, the MCB rating should be chosen to protect that size of cable. IE if it's a 1.5mm² flexible cable (fairly likely) the MCB should be changed to 16A. This is often reflected in the manufacturers instructions where they may state a 15 or 16A fuse or MCB. Manufacturers will of course deny responsibility if something goes wrong and their instructions have not been followed.
A lot of my work is maintenance and too many times I've seen the excessive damage as a result of a fault with incorrect protection.
As has been posted a 30mA RCD will trip much quicker on some faults than a MCB.
Personally I will change the MCB regardless of what the regs say.