We have recently had a Vaillant EcoTec Plus 428 installed (open vent, normal hot water tank) and we (myself and the installer) are trying to get it and the system configured. We get good heating performance, but when the heating is off and we only require hot water we are struggling.
The hot water cylinder is directly below the boiler, as cuch the piping run to it is very short, probably around 3m in total (1.5 flow, 1.5 return).
From it's coolest temperature, the boiler fires continuously for about 15/20mins, circulating and modulating to the set temperature (70 degrees). During this time the hot water in the tank reaches 40-45 degrees or so (target 55).
The boiler then drops into a cycle where it fires for 15-20secs before turning off, during the 'fired' time the flow temp quickly rises to the set temp. We know the 'anti-cycling' timer can be configured.
If the anti-cycle time is configured to 10 (so in reality the delay before re-fire is about 2-3mins), the flow temp drops to about 60, before the boiler fires again for 15secs or so. Doing this as long as no hot water is drawn, the tank will reach temp after about an hour during which time the boiler will fire and shut off about 15 times. Seems like that's a lot of firings and I'm sure at a previous house full temp was reached much sooner.
If the anti-cycle time is set much higher to 60 (so the delay before re-fire is about 11/12mins), the flow temp drops to about 50 before refire, but when refire happens the boiler still only fires for 20-30secs or so. Like this the tank hits temp after about 1.75 hours, but has only fired maybe 10-12 times.
The pump overrun is set such that the pump doesn't cut out between the cycles.
However we set it, after the initial firing (that lasts for a decent period), we can't seem to avoid the 'cycling' phase, the boiler won't again bring the flow temp up and hold it there without cutting out. Is this kind of behaviour to be expected? Or does it sound like something is amiss?
'Ranging' the boiler makes no difference in this scenario, it appears for the firing, the boiler doesn't begin to modulate until firing at full power for about 1 minute first. 'Ranging' doesn't appear to effect this initial 1 minute where it sounds like it's firing at the full 28kw power regardless.
Any hints, tips or suggestions gratefully received.
The hot water cylinder is directly below the boiler, as cuch the piping run to it is very short, probably around 3m in total (1.5 flow, 1.5 return).
From it's coolest temperature, the boiler fires continuously for about 15/20mins, circulating and modulating to the set temperature (70 degrees). During this time the hot water in the tank reaches 40-45 degrees or so (target 55).
The boiler then drops into a cycle where it fires for 15-20secs before turning off, during the 'fired' time the flow temp quickly rises to the set temp. We know the 'anti-cycling' timer can be configured.
If the anti-cycle time is configured to 10 (so in reality the delay before re-fire is about 2-3mins), the flow temp drops to about 60, before the boiler fires again for 15secs or so. Doing this as long as no hot water is drawn, the tank will reach temp after about an hour during which time the boiler will fire and shut off about 15 times. Seems like that's a lot of firings and I'm sure at a previous house full temp was reached much sooner.
If the anti-cycle time is set much higher to 60 (so the delay before re-fire is about 11/12mins), the flow temp drops to about 50 before refire, but when refire happens the boiler still only fires for 20-30secs or so. Like this the tank hits temp after about 1.75 hours, but has only fired maybe 10-12 times.
The pump overrun is set such that the pump doesn't cut out between the cycles.
However we set it, after the initial firing (that lasts for a decent period), we can't seem to avoid the 'cycling' phase, the boiler won't again bring the flow temp up and hold it there without cutting out. Is this kind of behaviour to be expected? Or does it sound like something is amiss?
'Ranging' the boiler makes no difference in this scenario, it appears for the firing, the boiler doesn't begin to modulate until firing at full power for about 1 minute first. 'Ranging' doesn't appear to effect this initial 1 minute where it sounds like it's firing at the full 28kw power regardless.
Any hints, tips or suggestions gratefully received.