Those numbers make no sense either for a running boiler, can you request HW and when cylinder stat calls for HW and the boiler starts note d40&d.41 again after say 5 minutes.
I would also change d.070 back to 0, its default setting, even though this parameter should have no function in a system (non combi) boiler.
I would also change d.070 back to 0, its default setting, even though this parameter should have no function in a system (non combi) boiler.