Well, if its happening like that and you still have 230V at the SL then does look like the fault is at the boiler end.The fault happens in both HW and CH, together or independently
Well, if its happening like that and you still have 230V at the SL then does look like the fault is at the boiler end.The fault happens in both HW and CH, together or independently
Have you ever purchased a refurbished pcb? They're alot cheaper but it's the risk of it not being new which are £250 circa.Well, if its happening like that and you still have 230V at the SL then does look like the fault is at the boiler end.
Yes was fine all week.Has the boiler been running OK since Mon last?
Why is a manual bypass needed or installed? it's a Y plan.
You renewed the pump very recently what make/model? UPS3?
After the pump but before the 3 port valve.The UPS3 even set to speed1 (4.2M) still circulates up to 12.5LPM at this head, 16.67LPM at a 3.6M head and 21.7LPM at a 3.0M head which should be quite adequate, you can allways change it to constant pressure CP 2 which will pump up to 32.5LPM at a constant 4.5m head but this may cause noise or pump over into the feed and expansion cistern if you have a open vented system.
Where is this manual bypass installed?.
Open vented.If you mean the brass/bronze valve immediately after (and another before) the pump, these are the pump (suction and discharge) isolating valves and are 1/4 turn ball valves, these should be fully open at all times except when changing out the pump.
The red wheel (gate) valve requires ~ 3 full turns to fully open and the same to shut, if this is currently shut and you try to open it (anticlockwise) then you will feel resistance initially then possibly no resistance for a 1/4 turn so and then moderate resistance while fully opening it. What is it bypassing?, it seems to be teed in just after the pump at one end..... whats at the other end?. Is it open or shut?.
It does look like a bypass between the boiler flow and return, might require say a turn open if you have TRVs installed.
Have you a open vented with a small feed&expansion cistern in the attic or a sealed system with a red expansion vessel somewhere?.
I've closed itIf its very hot then it is bypassing the water from the boiler flow (via the pump) back into the boiler return, can't really see any need for it with a 3 port valve.
Hi John,If its very hot then it is bypassing the water from the boiler flow (via the pump) back into the boiler return, can't really see any need for it with a 3 port valve.
The issue was likely due to poor conductivity.
They can't come loose over the years by themselves.If that fixed it, that would usually be described as poor connections, or terminations.
They can't come loose over the years by themselves.